The problem is society is not uniform in attitudes, education, and beliefs. While the UK is reasonably safety conscious in many ways, for example one of the lowest road death rates in Europe, we also have quite a capacity for stupidity as well.I agree. I,m also a little perplexed as the UK generally tends towards good order and pragmatism
701:555.05. "where a prefabricated shower cabinet is installed in a room other than a bath or shower room, any wall switch and any socket outlet shall be at a distance of at least 0.6 mts from the door opening of the shower or cabinet"
This reg is almost certainly "copied and pasted" from the UK. Its intention was to facilitate the likes of budget hotels that don't have the space to conform to the regs. It allows contractors dealing with unconventional domestic installs to assist customers with creative solutions.
Out of curiosity. 20,000 ohms in what scenario.? Would that be for instance a meter of 20mm plastic pipe full of rainwater, measured end to end?Rain vs wet hands is a bit different, but, at the same time, rain water has a resistance of 20,000 ohms.
Interestingly it seems tap water is far more conductive at 1000-5000 ohm.m from here:I think it's that rainwater has a resistivity of 20k ohm cm. (figures vary!)
Interestingly it seems tap water is far more conductive at 1000-5000 ohm.m from here:
Down to 200 ohm.m for brackish river water. Not sure what a bath filed with soapy stuff would be!![]()
Understanding the Resistivity of Water - Sensorex Liquid Analysis Technology
Understanding the resistivity of water is important for a number of reasons. This article discusses this and how you are able to measure it!sensorex.com
No, the RCD is still needed in my view unless you have eliminated single-fault risks.I am thinking that if disconnection time can be reduced to 0.17 seconds, the RCD is not needed from a safety sense. It would be nice is BS7671 took this into consideration.
No, the RCD is still needed in my view unless you have eliminated single-fault risks.
So if you have supplementary bonding then you have to have two "unobserved" faults before a short L-E becomes dangerous, both the original CPC and the supplementary bonding, to expose a person to a dangerous voltage. Up to the 16th (I think) that was the norm for wet areas in the UK.
If you only had the CPC and very fast OCPD then an open CPC fault leaves the person completely unprotected against a L-E fault.
Now that RCDs are cheap and readily available they should be used for all sorts of reasons. I still don't like depending on them as my primary means of disconnection due to the single "unobserved" fault risk (and higher probability of that than MCB sticking or fuse somehow failing to blow), but on any new systems they make sense as additional protection.
Agreed. An rcd as a primary means of protection never sat right. It's best suited to a "support role", basically plugging the holes that primary protection can't provide. It plays a supplementary but vital role.Correct, but as you say I do not like an RCD being the primary means to protect a user. In my opinion they supplemental or backup protection.
Agreed. An rcd as a primary means of protection never sat right. It's best suited to a "support role", basically plugging the holes that primary protection can't provide. It plays a supplementary but vital role.