What are the causes of unbalance current during no load test of transformer? | Page 2 | on ElectriciansForums

Discuss What are the causes of unbalance current during no load test of transformer? in the UK Electrical Forum area at ElectriciansForums.net

OK

Since you see the current between two phases on the delta winding, this means the one winding is either at fault, or (more likely) the secondary has a fault - I would guess one high voltage winding has a fault somewhere along its winding to earth (the star point being earthed) or has an inter-turn winding fault.

This phase will be the one corresponding to the branch of the delta connecting both current taking phases (~8A).

Can you flash test the hv windings - ~27-35kV as it may be an insulation breakdown issue, so won't be shown via an insulation resistance test?

If its an inter-turn winding fault it is a little more difficult to detect with an assembled tx.

(The above assumes there is absolutely nothing connected on the hv side - obviously if there is a single phase load/fault in that part of the system it will reflect as a phase-phase load/fault on the primary )
The star point is not earthed, All the transformer test results are satisfactory, Test we conducted are following;
IR (Both Windings), TTR, Open Circuit Test, Winding resistance
 

Reply to What are the causes of unbalance current during no load test of transformer? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
709
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
503
  • Question
Interesting. Sounds unusual since it seems it was very lightly loaded. Not much you can do I suppose other than buy a replacement unit. Unless...
Replies
7
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top