Yes, just asking the questionare you a spark?
It seems rather basicYes, just asking the question
One with a current carrying capacity greater than or equal to the rating of the breaker, with low enough impedance to ensure disconnection times are met and voltage drop is not too high, and greater than or equal to the load, which in turn should be less than or equal to the rating of the breaker.What size cable for 2 extractor fans in a public toilet?
Technically correct but somewhat unhelpfulOne with a current carrying capacity greater than or equal to the rating of the breaker, with low enough impedance to ensure disconnection times are met and voltage drop is not too high, and greater than or equal to the load, which in turn should be less than or equal to the rating of the breaker.
Of a type suitable for the conditions where installed.
Be careful mate. This is a public environment where literally anyone can come into contact with this work, and your neck is on the line as the bloke that installed it.What size cable for 2 extractor fans in a public toilet?
Thanks mate, I was just asking as someone’s done it and debating if they had installed the correct cable?Be careful mate. This is a public environment where literally anyone can come into contact with this work, and your neck is on the line as the bloke that installed it.
In the nicest way possible, if you need to ask this you shouldn't put yourself in the firing line.
That wasn't very clear from the question!Thanks mate, I was just asking as someone’s done it and debating if they had installed the correct cable?
Most domestic fan manufacturers require a 3amp inline fuse for their extractors and its normal to have a three pole isolation switch, one assumes this is in a work environment, therefore industrial/commercial?Total circuit load in amps?
Method C.At the moment my only answer is that no installation method of 3 core flat PVC 1.5mm cable is rated for 20 amps.
Strictly speaking method C is 19.5 amps. But we won't haggle over 0.5 of an amp. In fact running a 1.5mm directly to the 2 fans is also perfectly safe on a 20amp rcbo. But is it conventional, good practice or advisable? NoMethod C.