testing a house today before I put RCD protection on it and i got 300mA earth leakage. appox 100mA from the sockets, 180mA on the downstairs lighting circuit, then 20 odd mA accross the rest of the circuits.

I had a poke around the downstairs lighting circuit, couldn't see anything obvious, did R2 tests at all points (OK), did IR test and it was in the region of 650MΩ L-N, L-E and N-E.

as for the sockets, 2 chest freezers that are older then me are the cause of 50mA between them, rest is unnacounted for?

what causes this?
 
the really confusing issue is when the positrons decide to intervene. a traffic jam at the junction would ensue, causing road rage and the release of megajoules of energy, this could result in a massive meltdown of the supply cable and so we could all have the rest of the day in the pub
As long as its all on the old beer engines...forget about pumped....lol............
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
cumbria

Thread Information

Title
what causes earth leakage?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
82
Unsolved
--

Advert

Thread statistics

Created
ExArmy,
Last reply from
telectrix,
Replies
82
Views
67,353

Advert

TrueNAS JBOD Storage Server

Back
Top