I’m currently at the second fix stage of a rewire and before all the flooring goes down I’ve decided to do r1+r2 readings to make sure everything is continuous and polarity is correct. I also decided to do insulation resistance tests and have got lower than expected readings.

On the downstairs lighting circuit I got a reading of around 200-300Mohm. After breaking the lighting circuit down I found the reading was caused by the switch cable in the utility room however I can’t get to the entire length to inspect it. I might replace this one as it is a quick run.

I went to test a few radials circuits and they were perfect >1049Mohm. Went to do the upstairs ring and I was getting about 400Mohm Between neutral and earth.

Downstairs ring between live and earth I was getting around 600Mohm then it will climb to about 1000Mohm.

I know these readings are satisfactory as I’ve looked in the guidance note and it says minimum insulation resistance is 1Mohm but on a new install anything less than 20Mohm needs investigating.

I’ve read moisture is the main culprit and can be caused by damp from plastering, but it’s been plastered about 2 months ago.

There are no loads or sensitive equipment on the lighting circuits. On both rings there is a fused spur with no neon however I did forget to take the fuse out but that couldn’t cause these readings could it?

What else can cause readings to be lowered to these numbers?

I know guidance note 3 says less than 20Mohm is needs investigating but would you investigate if you got these readings or is it just over the top and a waste of time?
 
You've mentioned what I was going to mention - plaster, damp and moisture.
Even though we've had nice weather it takes a very long time for things to dry out.
You've also mentioned that the readings climb, and this suggests your test is drying it out.

It could even be that the cables have been stored somewhere damp before you fitted them.
I wouldn't waste any time looking further into those readings myself; on some houses I work on I'd give anything for those numbers!

Only other idea - were the fused spurs feeding anything with heating elements, and were the spurs switched on during the tests?
 
The results should be off scale new cable.when you say fused spur did you isolate them turn them off. You could be testing with loads still on.
 
You've mentioned what I was going to mention - plaster, damp and moisture.
Even though we've had nice weather it takes a very long time for things to dry out.
You've also mentioned that the readings climb, and this suggests your test is drying it out.

It could even be that the cables have been stored somewhere damp before you fitted them.
I wouldn't waste any time looking further into those readings myself; on some houses I work on I'd give anything for those numbers!

Only other idea - were the fused spurs feeding anything with heating elements, and were the spurs switched on during the tests?
Hmm you might be right about the moisture on this job as the house has been stripped apart. Theres been no heating since January. Only temporary sockets which the plasters used to power some little heaters to dry the plaster out with the windows open. The cables were also stored in the house when installing which was in January.

Both fused spurs are feeding a single socket which has nothing plugged into at the moment. One is unswitched and the other is switched but I cannot remember if it was switched on will need to do the test again tomorrow. The fuse has been left in both spurs but I can’t imagine this would affect the IR readings?

I’m just a bit baffled as on the switch cable the IR reading was only reading low between the live feeding the switch and earth. And on the rings, one ring the low reading was between L and E the other ring was between N and E as opposed to both L and E and N and E
 
The results should be off scale new cable.when you say fused spur did you isolate them turn them off. You could be testing with loads still on.
When you say off scale do you mean greater >999Mohm or what ever the figure is depending on the MFT being used?

one of the fused spurs cannot be isolated as its unswitched, I should have taken the live out the load side and put it in the supply side to bypass the fuse. And the other fused spur is switched but I did not turn it off and not sure if it was on or off to be honest.

There are no actual loads such as tv, washing machine etc plugged in at the moment
 
When you say off scale do you mean greater >999Mohm or what ever the figure is depending on the MFT being used?

one of the fused spurs cannot be isolated as its unswitched, I should have taken the live out the load side and put it in the supply side to bypass the fuse. And the other fused spur is switched but I did not turn it off and not sure if it was on or off to be honest.

There are no actual loads such as tv, washing machine etc plugged in at the moment
Yes
 
The switched cable I cannot investigate unless I cause damage to the ceiling instead of doing that I’m thinking of just replacing the cable it will be way easier.

But the rings, do you think that the 13A fuse in the spurs would cause the lower IR readings? There are no other loads on these circuits. There are no neons on the spurs
 
Yeah you’re right. I’m over thinking it. Thank you for the reassurance.

Out of curiosity what would cause these less than expected >1049Mohm readings on new cables/rewire?
You could test a length of cable which you can access end to end and take a reading just to see what reading you get. That's what I would do to satisfy me.
 
May not be the cables could be an accessory that has been contaminated.
the switch cable which I was getting about 200-300Mohm between the permanent live and Earth I disconnected from the accessories and still got the same reading which kinda bugs me.

Being contaminated for the ring circuits is a possibility as they have been filling around the sockets and sanding etc
 
Put it this way; if you had used a Megger 15xx, the ring circuit readings would have off the scale as it only goes up to 299M at 500v.
I've spent all day getting a circuit from 0.00M to 5M before now and gone home pretty happy!
Agree, the Dilog tester I have only goes up to 200M these readings are fine!
 
If you are seeing several 10Ms or more, and especially if it increases as you keep the test voltage on it, then I would not worry.

Edit: Look up "Polarisation Index" or "Dielectric Absorption Ratio" if you want some more info.
 
Last edited:
I was at the other end of the results spectrum today.
As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf and not the simplest to work for. She lives alone in a large detached town house. Consumer unit is in "the cats room", I gave serious thought to bringing some 20mm conduit in to breathe through.
Anyway, right hand RCD wouldn't stay on. Quickly traced to socket circuit, 0.00M.
After shouting various questions and getting nothing very useful back I worked out which sockets were served, unplugged things one at a time, and unplugging an extension lead caused a leap to 27M. That will do for 6pm when she's made it very clear she's waiting to watch Wimbledon.
"Oh yes I was mowing the lawn when it happened". (nice of you to mention it afterwards)
 

Reply to What causes low IR readings? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Big tv and gaming pc for sale. Both work, honest. 😉
Replies
4
Views
1K
  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
So the only thing you did was unscrew the sockets from the backplates? Are these backboxes galvanized? Do they have a rubber grommet where the...
Replies
4
Views
1K
  • Question
Yeah it was at the top of the board in a small cupboard and was a bit of a mess of cables. I was only doing an EICR on the one circuit and given...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks