I came across this earlier this week doing an EICR and would value your opinions on this matter.
I have occasionally been given a CU to install only to arrive and find the switch is on the wrong side of the CU and it will not fit in the current configuration. I was taught to move the switch and RCD positions, switch live and neutral inputs and outputs on the main switch and RCD’s meaning the live feed out of switches and RCD’s is directly next to any MCB’s. (hope this makes sense)
Is that good practice? What do others do?
This is what I found earlier this week. Note the live and neutral into the RCD and consider the busbar feeding the MCB’s.
See photo
The installer got round the issue of the neutral output from the RCD’s being between the live output and the MCBs by taking the Busbar from the live output, cutting of the tab that would have gone into the neutral output and then onto the MCB’s. I consider this incredibly dangerous. If you consider the neutral stranded cables out of the RCD is now crushed by the busbar and plastic cover that will not seat fully because it is interfered with by the protruding neutral cable.
See second Photo
Both the live and neutral outputs of the RCD are only protected by the 100A service fuse. In the event of a fault causing heat, there could be a huge bang if the plastic separating the neutral from the busbar melts.
I have occasionally been given a CU to install only to arrive and find the switch is on the wrong side of the CU and it will not fit in the current configuration. I was taught to move the switch and RCD positions, switch live and neutral inputs and outputs on the main switch and RCD’s meaning the live feed out of switches and RCD’s is directly next to any MCB’s. (hope this makes sense)
Is that good practice? What do others do?
This is what I found earlier this week. Note the live and neutral into the RCD and consider the busbar feeding the MCB’s.
See photo
The installer got round the issue of the neutral output from the RCD’s being between the live output and the MCBs by taking the Busbar from the live output, cutting of the tab that would have gone into the neutral output and then onto the MCB’s. I consider this incredibly dangerous. If you consider the neutral stranded cables out of the RCD is now crushed by the busbar and plastic cover that will not seat fully because it is interfered with by the protruding neutral cable.
See second Photo
Both the live and neutral outputs of the RCD are only protected by the 100A service fuse. In the event of a fault causing heat, there could be a huge bang if the plastic separating the neutral from the busbar melts.