I came across this earlier this week doing an EICR and would value your opinions on this matter.

I have occasionally been given a CU to install only to arrive and find the switch is on the wrong side of the CU and it will not fit in the current configuration. I was taught to move the switch and RCD positions, switch live and neutral inputs and outputs on the main switch and RCD’s meaning the live feed out of switches and RCD’s is directly next to any MCB’s. (hope this makes sense)

Is that good practice? What do others do?


This is what I found earlier this week. Note the live and neutral into the RCD and consider the busbar feeding the MCB’s.

See photo

The installer got round the issue of the neutral output from the RCD’s being between the live output and the MCBs by taking the Busbar from the live output, cutting of the tab that would have gone into the neutral output and then onto the MCB’s. I consider this incredibly dangerous. If you consider the neutral stranded cables out of the RCD is now crushed by the busbar and plastic cover that will not seat fully because it is interfered with by the protruding neutral cable.

See second Photo

Both the live and neutral outputs of the RCD are only protected by the 100A service fuse. In the event of a fault causing heat, there could be a huge bang if the plastic separating the neutral from the busbar melts.

IMG_0453.JPG


20170606_151957.jpg
 
I generally fit either BG or MK as they have the main switch at opposite ends, but then I always visit site first. Whoever is giving you CU's to fit, you need to bring it up with them as to why they haven't made an allowance for the switch position or new tails.
 
I fitted a new MK Sentry board at home and it was configured the wrong way, so I disassembled it and reassembled it so it would work, ensuring none of the internal cables were under undue strain. I certainly wouldn't do what's shown in pic #2 as that does appear to be a disaster waiting to happen.

Fitting new tails wasn't really an option because they are in the cavity and I didn't want the headache of opening a new cable exit point in the wall or chasing the wall out to accommodate them as there were already cables in the wall.

I don't see a problem with tweaking the layout of the board, it's just like buying an empty board and filling it yourself.
 
I think I would have put new mains tails in.

The example I had when gaining experience was an SWA feed through a wall to a sub board that we were changing, so not practical to extend tails.

I do make sure I have the right CU for replacement, but is switching things around and making sure the live output is in the correct position for Bus Bars considered acceptable or should the CU be taken back and changed it for a more suitable one?
 
Henley block and extend tails is a far easier solution

In this case, a Henley block would have meant repositioning the CU and extending all circuits, so not practical.

Replacing tails would have meant tails come in on the left, and run the entire length of the CU to the switch on the right. I would not be comfortable with that if it were my job.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Amersham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What do folk do when given a CU with switch on wrong side?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
40
Unsolved
--

Advert

Thread statistics

Created
Davisonp,
Last reply from
stevethesparks,
Replies
40
Views
6,897

Advert

Back
Top