Hello, I am a woodworker who has got a large old power feed, its 380v and i want someone to rewire to a 220v vfd for me, can someone please tell me what these old colour codes mean. I bought the machine in Scotland.I can't find any easy diagrams online.I think its a good few years old.Thank you!

1 2 3 4 5 6 7
 
On the subject of the original motor, I've missed a trick. I'm convinced now it's a Dahlander consequent pole 2-speed motor, which runs in double-star at full speed and in series delta at low speed with equal torque. You won't need the low speed mode as the VSD will do that for you, so you could run it on a 230V inverter by swapping the internal interconnections between the two winding groups so that the same relative coil polarities as are currently obtained in star are obtained in delta instead. That would give you a single-speed, 230V delta motor of full power rating. If you wanted to go down this route, I would need to see very detailed pics of the internal winding leadouts, and we would have to pick through them with a continuity tester very carefully to ensure we make the right interconnections.
 
On the subject of the original motor, I've missed a trick. I'm convinced now it's a Dahlander consequent pole 2-speed motor, which runs in double-star at full speed and in series delta at low speed with equal torque. You won't need the low speed mode as the VSD will do that for you, so you could run it on a 230V inverter by swapping the internal interconnections between the two winding groups so that the same relative coil polarities as are currently obtained in star are obtained in delta instead. That would give you a single-speed, 230V delta motor of full power rating. If you wanted to go down this route, I would need to see very detailed pics of the internal winding leadouts, and we would have to pick through them with a continuity tester very carefully to ensure we make the right interconnections.

:)You're Brilliant! if you're up for a challenge I can follow your instructions to a tee,its a beast of a power feed, aprox 120 kg. I will need to get a mulitmeter/continuity tester, I presume I need to unmount from the gearbox and open it up and take pics of the windings?
Im a trained engineering technician but complicated electrics not my forte:)
 

Attachments

  • [ElectriciansForums.net] what do these 380v wiring colours mean, I want to use with a 220v vfd. it may have had speed control
    this_is_the_final_destination_).png
    238.8 KB · Views: 26
Disclaimer:
Some time will need to be invested to find out whether it is possible at all.
There is a high risk of accidental error with the windings as there are millions of permutations of 12 wires (six windings each with two ends). If they get mixed up or we mis-identify them, it will be slow and tricky to identify the proper phasing again without specialist equipment. Getting one winding out of phase for example, could result in poor torque, blown fuses, burnout, inverter destruction or all of the above. So proceed at your own risk.

As there only seems to be one lead from inside the motor to each terminal stud (please confirm), the connections must be within the end bell so you would have to get inside there to swap them over. If they are hidden or bound up with winding tape it could be tricky. I suppose you've nothing to lose by looking inside though.

@marconi @Marvo @darkwood and anyone else please check my logic:

a) It has to be a Dahlander connection as-is.
b) There are 6 leads in the terminal box for 12 winding ends so they must be paired internally into series delta.
c) The edges of the delta (2U, 2V, 2W) can remain connected as-is, as this gives the right relative polarity of both windings of each phase for high-speed.
d) The corners of the delta (1U, 1V, 1W) need to be split so that the two windings of each phase can be paralleled.
e) The paralleled windings can then be connected in delta to make a 3-lead 230V motor.

One snag we have now is that we don't know for certain which set of leads are the edges and which are the corners. We might assume that terminal block 1U= winding U1 = corner terminal etc but there's no guarantee because the original speed switching has been disconnected. If we can see the windings leading out from their respective coils, that's fine. Otherwise we might have to use a battery and compass in the bore, or feed in low voltage AC e.g. from a bell transformer and find coil phasing by searching with a voltmeter.

I'll post a diagram later.
 
Last edited:
Disclaimer:
Some time will need to be invested to find out whether it is possible at all.
There is a high risk of accidental error with the windings as there are millions of permutations of 12 wires (six windings each with two ends). If they get mixed up or we mis-identify them, it will be slow and tricky to identify the proper phasing again without specialist equipment. Getting one winding out of phase for example, could result in poor torque, blown fuses, burnout, inverter destruction or all of the above. So proceed at your own risk.

As there only seems to be one lead from inside the motor to each terminal stud (please confirm), the connections must be within the end bell so you would have to get inside there to swap them over. If they are hidden or bound up with winding tape it could be tricky. I suppose you've nothing to lose by looking inside though.

@marconi @Marvo @darkwood and anyone else please check my logic:

a) It has to be a Dahlander connection as-is.
b) There are 6 leads in the terminal box for 12 winding ends so they must be paired internally into series delta.
c) The edges of the delta (2U, 2V, 2W) can remain connected as-is, as this gives the right relative polarity of both windings of each phase for high-speed.
d) The corners of the delta (1U, 1V, 1W) need to be split so that the two windings of each phase can be paralleled.
e) The paralleled windings can then be connected in delta to make a 3-lead 230V motor.

One snag we have now is that we don't know for certain which set of leads are the edges and which are the corners. We might assume that terminal block 1U= winding U1 = corner terminal etc but there's no guarantee because the original speed switching has been disconnected. If we can see the windings leading out from their respective coils, that's fine. Otherwise we might have to use a battery and compass in the bore, or feed in low voltage AC e.g. from a bell transformer and find coil phasing by searching with a voltmeter.

I'll post a diagram later.
Mega cool of you and the forum! I fully accept this might not be possible or work at all. I will get to work removing it from gearbox and sharing all the info depth info u need. I wanted to know more about motors, this is a premium learning exercise!
X mas is coming up fast, understand if this waits until NY. Again amazingly cool of you and the forum. :)
 
wow, you are getting not beyond my understanding but certainly out of my comfort zone.

not sure if I understand correctly what you are referring to when describing the windings but have got as far as this poorly drawn representation. left (as is) right (convert to)

am I with you so far?

its been a long time since I was sat in a hall figuring out if it was the left hand or right hand that I should be putting into silly positions for the solution.
 

Attachments

  • [ElectriciansForums.net] what do these 380v wiring colours mean, I want to use with a 220v vfd. it may have had speed control
    IMG_1223.jpg
    62.6 KB · Views: 26
I reckon you have this motor winding set up(Dahlander/pole changing) as in the attachment.

The six wires are brought out to the 6 terminals as the triplets 1V, 1U and 1W and 2U, 2V and 2W and connected as in the diagram at attachment.

To effect pole changing one swaps the 3 lines L1, L2 and L3 between these triplets and when the lines are connected to 2U, 2V and 2W one connects 1U, 1V and 1W together.

3 Lines to the series delta is for slow speed by making an 8 pole(4 pole pairs) machine with speed of 750 rpm and 3 lines in parallel star for 4 pole (2 pole pairs) with sync speed of 1500 rpm.
[automerge]1576526838[/automerge]
The motor terminal is:
W2 U2 V2
U1 V1 W1

but photographed upside down

W1(Blue) V1(Green) U1(Orange)
V2(Brown) U2(Black) W2(Gray/Light Brown)
 

Attachments

  • woodfeedermotor.docx
    15 KB · Views: 11
Last edited:
I reckon you have this motor winding set up(Dahlander/pole changing) as in the attachment.

The six wires are brought out to the 6 terminals as the triplets 1V, 1U and 1W and 2U, 2V and 2W and connected as in the diagram at attachment.

To effect pole changing one swaps the 3 lines L1, L2 and L3 between these triplets and when the lines are connected to 2U, 2V and 2W one connects 1U, 1V and 1W together.

3 Lines to the series delta is for slow speed by making an 8 pole(4 pole pairs) machine with speed of 750 rpm and 3 lines in parallel star for 4 pole (2 pole pairs) with sync speed of 1500 rpm.
[automerge]1576526838[/automerge]
The motor terminal is:
W2 U2 V2
U1 V1 W1

but photographed upside down

W1(Blue) V1(Green) U1(Orange)
V2(Brown) U2(Black) W2(Gray/Light Brown)

thanks very much!

does that mean that this is not a
star delta wired motor? or that is the same as a
Dahlander/pole changing

how does the pole changing happen? is it in a fixed position by replacing physical wires or a switch of somekind?
 
The motor terminal is:
W2 U2 V2
U1 V1 W1

but photographed upside down

W1(Blue) V1(Green) U1(Orange)
V2(Brown) U2(Black) W2(Gray/Light Brown)

SpeedtStu - As LN said and I concur, the motor windings are arranged for (Dhalinder pole change )and not star then delta for start then run operation. Could you tell us how many internal wires are attached to each terminal - it looks like only one indicating as LN said that there are internal connections between "2U-2V, 2V-2W and 2U -2W; but they may be other connections under the terminal block. Could you undo the two chrome slotted screws and have a look underneath for any more connections?

Otherwise the motor will have to opened up to access these pairings, severe them and reconnect them differently to form a parallel delta arrangement of windings able to be energised at 230V line-to-line.

Sorry rushed at the moment have to go picj the wife up from choir practice - the pole chamging is done by switching the incoming 3 lines between tge triplets I mentioned earlier and when in one of those configurations connecting together three nodes as I mentioned. If yu stare at the doagram I showed and imagined defroning it by pulling 2U, "2V and 2W in three directions angles 120 degrees apart away from the controid you can see how it can swap between series delta and parallely star and the 1U and 1W and 1U vertices come together .
 
Last edited:
The motor terminal is:
W2 U2 V2
U1 V1 W1

but photographed upside down

W1(Blue) V1(Green) U1(Orange)
V2(Brown) U2(Black) W2(Gray/Light Brown)

SpeedtStu - Could you tell us how many internal wires are attached to each terminal - it looks like only one indicating as LN said that there are internal connections between "2U-2V, 2V-2W and 2U -2W; but they may be other connections under the terminal block. Could you undo the two chrome slotted screws and have a look underneath for any more connections?

Otherwise the motor will have to opened up to access these pairings, severe them and reconnect them differently to form a parallel delta arrangement of windings able to be energised at 230V line-to-line.
i will do that tomorrow in good light, i can do all of the above with instructions. You're all superstars!
 
See attached image first.

If one takes the transform of the star configuration to the delta configuration
and use the nomenclature u1 and u2 as the start an ends of U1 and u3 and u4 as the start and ends of winding U2 - similarly for V1, V2, W1 and W2, then for star

L1 - u1, L2 - v1, L3- w1 and star is u2 - v2 - w2.

Transforming to delta the winding ends are connected:

L1 - u1 and L2 - u2
L2 - v1 and L3 - v2
L3 - w1 and L1 -w2

If one uses the same transform for the parallel star arrangement to a parallel delta arrangement one has for star:

L1 - u4 - v1
L2 - v4 - w1
L3 - w4 - u1

and star point is u2 - u3 - v2 - v3 - w2 - w3

which transforms to a delta of:

L1/2U terminal - u2 - w3 - (u4 - v1)
L2/2V terminal - v2 - u3 - (w1 - v4)
L3/2W terminal - v3 - w2 - (u1 - w4)

where the winding ends in brackets () are already connected as required to L1, L2 or L3 but those not in brackets viz u2, u3, v2, v3, w2, w3 are not connected as required. At the moment the connections are made (u2-u3), (v2-v3) and (w2-w3) which are the corners of the low speed delta configuration. As Lucien said these pairings need to be accessed, severed and reconnected as shown above in bold.

Or I have made a complete Horlicks..... :)
 

Attachments

  • [ElectriciansForums.net] what do these 380v wiring colours mean, I want to use with a 220v vfd. it may have had speed control
    main-qimg-00f1fd9601d8cc9892f5db6358289db4.png
    48.2 KB · Views: 17
Last edited:
See:

How to connect 3 phase motors in star and delta connection - Quora - https://www.quora.com/How-do-I-connect-3-phase-motors-in-star-and-delta-connection

If one takes the transform of the star configuration to the delta configuration
and use the nomenclature u1 and u2 as the start an ends of U1 and u3 and u4 as the start and ends of winding U2 - similarly for V1, V2, W1 and W2, then for star

L1 - u1, L2 - v1, L3- w1 and star is u2 - v2 - w2.

Transforming to delta the winding ends are connected:

L1 - u1 and L2 - u2
L2 - v1 and L2 - v2
L3 - w1 and L1 -w2

If one uses the same transform for the parallel star arrangement to a parallel delta arrangement one has for star:

L1 - u4 - v1
L2 - v4 - w1
L3 - w4 - u1

and star point is u2 - u3 - v2 - v3 - w2 - w3

which transforms to a delta of:

L1/2U terminal - u2 - w3 - (u4 - v1)
L2/2V terminal - v2 - u3 - (w1 - v4)
L3/2W terminal - v3 - w2 - (u1 - w4)

where the winding ends in brackets () are already connected as required to L1, L2 or L3 but those not in brackets viz u2, u3, v2, v3, w2, w3 are not connected as required. At the moment the connections are made (u2-u3), (v2-v3) and (w2-w3) which are the corners of the low speed delta configuration. As Lucien said these pairings need to be accessed, severed and reconnected as shown above in bold.

Or I have made a complete Horlicks..... :)
I am sorting out a multimeter as you guys wow me again, this is very cool of you all. I'll do my best to pull it off. Thanks again!
 
Lucien: My analysis indicates that the windings (U1, V1, W1) are wound in the same way so that the same current flowing from 1 to 2 produces the same direction of magnetic field.

The windings (U2, V2, W2) are wound in the opposite direction to U1, V1, W1 which means to produce the same direction of magnetic field as U1, V1, W1 the current must flow 4 to 3.

To produce a conventional pole pairs using parallel delta, the windings (UV, UW, VW) are connected in parallel by connecting 1 to 4 and 2 to 3; this creates the same direction of magnetic field in each coil. This is what is seen in my #25 (if you draw it out - see my scribbled attachment and note #). The current flow then through say the pair V1 and W3 is in opposite directions but the coils are wound opposite way to each other so magnetic field combine. The Ampturns of V1 and W3 are in the same direction.

This is just what we want for the 230V line to line parallel delta configuration for the creation of conventional pole pairs (high speed).

As a quick check slow speed by consequent pole generation would now be series star but require 400V line to line and the coils would be connected in series as say u1 U1 u2 w3 W2 w4.

Note #: The arrows indicate the magnetic field direction for current flows 1 to 2 or 3 to 4.

I could have made a mistake though so do point it/them out to me ....
[automerge]1576570129[/automerge]
wow, you are getting not beyond my understanding but certainly out of my comfort zone.

not sure if I understand correctly what you are referring to when describing the windings but have got as far as this poorly drawn representation. left (as is) right (convert to)

am I with you so far?




James - see attachment in my #26. LN is suggesting (cleverly) converting the 380V line to line parallel star high sync speed winding configuration as is (-you showed a series star) into a to be 230v line to line parallel delta (which you did draw).
 

Attachments

  • [ElectriciansForums.net] what do these 380v wiring colours mean, I want to use with a 220v vfd. it may have had speed control
    deltadelta.JPG
    105.1 KB · Views: 12
Last edited:
Crikey, I was only asking for a yes or no!
I'll look later, I have two machine breakdowns which are holding a job up.

In the meantime, I'll add a note about safety. If the original controls are missing and being replaced by the inverter, you are modifying the machine in a safety-critical way. There are all sorts of regulatory implications if you use the machine in a place of work or sell it. If the new controls and mode of operation are not compliant (and proven to be compliant), it may be a breach of various regs to install, operate or sell it. I will leave all those implications for you to work out. My only interest here is to investigate the motor and identify whether it can be reconfigured to run on 230V.
 
Crikey, I was only asking for a yes or no!
I'll look later, I have two machine breakdowns which are holding a job up.

In the meantime, I'll add a note about safety. If the original controls are missing and being replaced by the inverter, you are modifying the machine in a safety-critical way. There are all sorts of regulatory implications if you use the machine in a place of work or sell it. If the new controls and mode of operation are not compliant (and proven to be compliant), it may be a breach of various regs to install, operate or sell it. I will leave all those implications for you to work out. My only interest here is to investigate the motor and identify whether it can be reconfigured to run on 230V.
Thanks everything so far. To confirm this will only be used in my own private workshop :) I've ordered a multimeter today and will start getting all the pics together, it would be a very cool project to work with you all on. Great piece of machinery to have working.
 
Fixed my breakdowns, one was an intermittent internal break in an encoder cable, other was a configuration problem.

You are correct that star-delta pole-changing is fundamentally different from star-delta starting. Star-delta starting is a method applied to a conventional 3-phase motor, while pole-changing is a function of a specially built 2-speed motor. What they have in common is the use of switching to rearrange the winding connections.

Star-delta starting is a basic soft-start method used with regular single-speed 3-phase motors that have one group of three windings rated for the full line-line voltage. When connected in star for starting, each 400V winding receives only 230V, reducing the starting current and torque. After a sufficient run-up time, the starter reconnects the windings into delta so that each winding receives the full 400V and full torque is available.

A pole-changing motor is specially constructed to deliver two speeds at the turn of a switch. The Dahlander configuration provides a simple and convienent way to alter the phasing and the voltage per winding with the minimum of switch contacts, suitable for motors with 2:1 speed ratio and windings rated for the line-neutral voltage. It does not offer a soft-start as such, which would require a more extensive switching system and probably be redundant on a typical small pole-changing motor.

Inverter drives make both techniques obsolete, because they can provide both soft starting and selectable fixed running speeds. For use with a 400V output inverter, a motor originally wired for star-delta starting can be left in delta (full power) and a Dahlander motor can be left in star (high speed) and controlled exclusively by the VFD. The standard motor could optionally be reconfigured for 690V in star, and the Dahlander motor 230V in delta, which is what we are looking to achieve here.
 

Reply to what do these 380v wiring colours mean, I want to use with a 220v vfd. it may have had speed control in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top