1Justin

-
Arms
Joined
May 20, 2011
Messages
497
Reaction score
169
Location
Surrey
I came across this at a customer's place.

[ElectriciansForums.net] what do you call this fuse?

Semi - enclosed ceramic but it pre-dates BS3036. The iron break-out (yes it is is bonded..) enclosure is "Callender" branded and dates from when the house was built (1930's).

I will pull the fuse next visit and measure/check the wire diameter. I am expecting 60A but not sure. The Callender brand ceramic holder says "Carry 30, 60 blow" but that will be pretty meaningless. The customer says the fuse blew some years ago and was replaced. (I have checked - it does contain a fuse and not a nail.

I could replace the wire next visit with known 60A so I can correctly document it ? - But that belongs to DNO and not my bit to alter. Would you do this - or just rely on the Vernier & 533.1.1.3 ? DNO seemed happy with the fuse (by visual inspection only isofar as there was one!) without even checking it - see later.

60 A is adequate for the customer (with a little constructive diversity) and is limited to that anyway by 16mm tails to the meter.

I shall probably assume the worst-case for short-circuit capacity of newer BS3036 S1A type (ie 1KA). - This still covers me for the measured PFC.

Installation is TNS, lead sheathed supply cable with double layer spiral steel banding.

I had the DNO round before touching anything to provide the installation with a new MET clamped to the lead sheath since first thing I did was measure 8 Ohms Ze. (There was no MET, and a teeny single strand Cu wire earthing conductor wrapped round the sheath and probably corroded) - Now a better figure Ze (0.33) from which to begin.

I was very surprised that DNO guy said they have changed their policy recently, and now they won't replace break-outs like this even if they are 80 years old.

But what type of fuse do I record? (For supply protective device in EIC) ? I could just put "semi-enclosed fuse", 60A (TBC after inspection), and assume 1KA rated short circuit capacity. - Would that be reasonable?
 
Last edited:
It's still classed as BS 3036 protection, as are all rewireable fuses.... By the way the arrangement shown in your photo say's it's TN-S not TNC-S...

The DNO shouldn't of been happy with this service cut-out, in fact they have been instructed to replace all such iron clad rewireable service heads nationwide by 2011, which they haven't complied with.
 
Last edited by a moderator:
To be honest I don't think there is a lot more you can really do, but cater for worse case here. Your take on it being S1A and 1Ka is pretty fair.

Not sure what you mean by it being an TNC? it is either a TN-C-S or a TN-S and by the looks of things it is certainly not a TN-C-S. What was your Ze reading by the way?
 
What was your Ze reading by the way?


Stated in the OP's post mate!! lol!!

first thing I did was measure 8 Ohms Ze. (There was no MET, and a teeny single strand Cu wire earthing conductor wrapped round the sheath and probably corroded) - Now a better figure Ze (0.33) from which to begin.


Yep, first thing you need to do on your next visit home, is a trip to SpecSavers!! lol!!
 
ooops typo guys sorry I did mean TNS when I wrote it. Corrected now to save future confusions..

Thanks for the comments.

It's interesting to hear from Engineer 54:


The DNO shouldn't of been happy with this service cut-out, in fact they have been instructed to replace all such iron clad rewireable service heads nationwide by 2011, which they haven't complied with.
 
ooops typo guys sorry I did mean TNS when I wrote it. Corrected now to save future confusions..

Thanks for the comments.

It's interesting to hear from Engineer 54:

Too late I'm afraid
I have had to meticulously read each sentence to find the offending words and failed but all has now been revealed lol
 
pre-empted by ezzz. was going to say that i once had a fuse like that and called it albert, just because it looked victorian.
 
I am happy to don my big yellow gloves and pull a fuse but I personally would leave that, I'd worry it would break in my hand. I'd be much happier if it was changed, are you sure you cant smell what you think is burning lol, and while they are there...
 

Reply to what do you call this fuse? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top