OP
Engineer54
The LV main is the cable originating in the substation that all supplies will be breached from. it is run as a radial configuration sometimes with the option to be backfed or backfeed other LV mains via link disconnector boxes.
Any joint or repair carried out on a paper lead distribution cable will have neutral and earth connected together in that joint. They will already be connected at the substation and every main will have been PME'd at some point in the past. When a paper lead main or service is repaired wavecon CNE cable or hybrid will be used (3 core and copper neutral/earth 3 phase and 1 core and copper neutral/earth for single phase. On new supplies a rod must be installed every 40m (if there are joints) or before the last 4 properties on that main. This is to reduce the amount of customers affected by a neutral fault.
TN-S can be supplied from a PME'd main as previously mentioned, this is current practice on new installs with multiple supplies to steel framed buildings. This is to stop circulating currents in the frame. Alternatively no earth will be supplied and TT will most likely be used.
All the above is based on my knowledge of the DNO in my area and other areas may work to different practices.
Thanks for the reply mechelec,
Have read you post several times, and can't see how a neutral fault on the PME side can't be transmitted to any of the TN-S customers earthing terminals. That S in TN-S stands for ''separate'' which it clearly isn't in your explanation/description, if both joints and PME'd service heads are N-E linked throughout the system. That especially goes for supplying a TN-S from a CNE cable. Can you describe how that is achieved, as i just can't get mind straight on that one....
I understand the process of PME'ing new underground supplies, they will generally be done to the book, it's the converting of the older TN-S supply cables that sometimes leaves a lot to be desired, and that is almost always down to cost implications.
Now i maybe missing something here in all this, by not letting my thinking have some rope so to speak, so any clarification on your part, or misguidance on my part that you can see, will be gratefully welcomed.