Hi to all. I'm new and this is my first post.
I'm doing an EICR on a 3 story building split into multiple offices to let.
One thing I noticed is t+e cables in plastic trunking almost throughout (switch/socket drops, across ceilings to lights etc).
Would this be a code 2 or 3? Also would same code be throughout or just in escape routes?
I understand it could potentially be dangerous (causing entanglement when melting/falling etc), but surely an EICR is regarding electrical safety and as far as I can see the installation is electrically safe!
Any views as it would be a massive job to correct.
Surely if its a C2 then most commercial buildings in the country would fail?
Should I just C3 it and suggest landlord gets a fire safety report done?
 
There was an exception to omit RCD protection for cables concealed in walls if the installation was under the control of a skilled or instructed person.
There was also an exception to omit RCD protection for socket-outlets if their use by ordinary persons was supervised by a skilled or instructed person.
 
C2? rollox, there would be hundreds of millions of pounds worth of urgent work required in hundreds of thousands of properties, C3 at best, it was perfectly safe before they updated the Regs lol, the world wasn't going to end then.
 
We had a seminar today from one of the surveyors, which was largely about fire safety.
Apparently (unlike BS7671) fire regulations are retrospective, hence lack of fire resistant supports being a C2 and not a C3. I suppose the logic behind this is the best person to rectify it would be an electrician.
 
C2? rollox, there would be hundreds of millions of pounds worth of urgent work required in hundreds of thousands of properties, C3 at best, it was perfectly safe before they updated the Regs lol, the world wasn't going to end then.
Tell that to the fire fighters families who lost loved ones due to falling cables and being entangled in them as a resulting investigation concluded that the death of a few fire fighters was caused by said entanglement hence the introduction of the regulation.
I think millions of properties is a bit far considering the requirement is escape routes only and 99% of the time domestic dwellings are not an issue due to the plaster board integrity of the ceilings.
I am all for the regulation and even the new requirement due out when the 18th edition is in full effect.
 
Bollox, the regs have changed thats all, no doubt some fire fighters have seen problems with wires hanging down, but I would say it is minimal, same as plastic DBs, there are millions, but one catches fire and suddenly they all need to be metal. I never said millions of properties, hundreds of thousands I said, open your eyes.
 
Last edited by a moderator:
Bollox, the regs have changed thats all, no doubt some fire fighters have seen problems with wires hanging down, but I would say it is minimal, same as plastic DBs, there are millions, but one catches fire and suddenly they all need to be metal. I never said millions of properties, hundreds of thousands I said, open your eyes.
Hundreds of thousands then happy now?
The relevance of the regulation has obviously passed you by.
Wires hanging down!!
 
Last edited by a moderator:
I'm aware of the reasons of the regulation, and I understand why the regulation has been put into the bible, but coding a new regulation failure as a C2 which means action is required is total bollox, it must be a C3, I don't care what they suggest, if we coded every new reg which was not up to the latest ammendment as a c2 we would all need to have our homes rewired every 2 years. Regarding telling it to the families, even one fire fighter dying is a tragic, but seriously how many have died due to this? it cannot be so dangerous all of a sudden to make it a C2, if the case then insurance companies must refuse to insure houses, as they are not safe to live in, again total bollox.
 
Bollox, the regs have changed thats all, no doubt some fire fighters have seen problems with wires hanging down, but I would say it is minimal, same as plastic DBs, there are millions, but one catches fire and suddenly they all need to be metal. I never said millions of properties, hundreds of thousands I said, open your eyes, dick wipe.
Their names were Jim Shears and Alan Bannon.
This isn't someone's perception or scaremongering, it was an actual thing which happened, at Shirley Towers in Southampton:
Fire deaths lead to safety change - http://www.bbc.co.uk/news/uk-england-hampshire-30845937
Perhaps this is only seen as an important issue around here due to it's proximity.
 
As I said even one death a tragic situation, but lets be sensible here, as I said vertually every house in the country could be considered dangerous if cabling not secured properly near entrances and exits, the IEE, IMO have done right by including this new reg into the bible, but a C2 for this, nah not in my view, a C3 yes, but not a C2, total bollox.
 
It doesn't have to be a big job though Mike - a catenary wire spanned above a suspended ceiling with a few metal cable ties on it, and lives could be saved. What is so bad about that?
 
The idea of the reg as I have said is a good one, I am all for it, but telling thosands of people their homes are suddenly dangerous and not insurable due to a new reg stinks IMO, I understand all new homes need to adhere to this, and agree with it, but when a EICR is carried out on a home for sale for example and this is put in as a c2, it means the house need to have work done to it before it can get sold and that IMO due to a new reg is wrong, the coding should be a C3 not up to current regulations and no more.
 
I'm aware of the reasons of the regulation, and I understand why the regulation has been put into the bible, but coding a new regulation failure as a C2 which means action is required is total bollox, it must be a C3, I don't care what they suggest, if we coded every new reg which was not up to the latest ammendment as a c2 we would all need to have our homes rewired every 2 years. Regarding telling it to the families, even one fire fighter dying is a tragic, but seriously how many have died due to this? it cannot be so dangerous all of a sudden to make it a C2, if the case then insurance companies must refuse to insure houses, as they are not safe to live in, again total bollox.
In the 60s lighting circuits here not required to have cpc’s installed.
I can only assume common sense or perhaps the amount of people receiving electric shocks prompted a drastic safety improvement.
Would you C3 this if exposed conductive parts where connected to the circuit without a cpc present?
As for the fire fighters, a change to the regulation and actually identifying a potential risk and danger may just save someone’s life during a fire and I think that’s worth it.
What’s someone’s life worth to you?
 
we are not talking about cabling without CPCs, and do not insult my intelligence about asking what I think someones life is worth, I have clarified my view.
 
Last edited by a moderator:

Reply to What EICR code for plastic trunking in escape routes? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

I don't think anyone on here is going to say it needs replacing, some may even argue that it's not even a c3.
    • Like
Replies
3
Views
427
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
444

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top