Just processing an EICR and noticed a couple of final circuits measured Zs values (fed from a sub distribution board) slightly exceed the Max permitted Zs values for the OCPDs that protect them.
Obviously I will note this as a design flaw in the observations, but I just wondered, from the perspective of ADS, as the circuits are also protected by a 30Ma RCD, does this negate the need to fully consider Maximum permitted Zs values for the OCPDs?
Is it not deemed that the fault protection in this event could be being provided by the RCD?
After all, if the earthing system was TT the measured Zs values would be way higher than the Max permitted for the devices...
Cheers
Spud.