spud1

-
Arms
Joined
Oct 23, 2010
Messages
354
Reaction score
54
Location
Somerset
Just processing an EICR and noticed a couple of final circuits measured Zs values (fed from a sub distribution board) slightly exceed the Max permitted Zs values for the OCPDs that protect them.

Obviously I will note this as a design flaw in the observations, but I just wondered, from the perspective of ADS, as the circuits are also protected by a 30Ma RCD, does this negate the need to fully consider Maximum permitted Zs values for the OCPDs?

Is it not deemed that the fault protection in this event could be being provided by the RCD?

After all, if the earthing system was TT the measured Zs values would be way higher than the Max permitted for the devices...

Cheers

Spud.
 
On a TT system a do a Zn to ensure the circuit OCPD would disconnect in time for short circuit conditions, then Ze to ensure the circuit would meet the requirements for RCD protection.

On a TN if the readings were just over and the circuit was designed and installed to pre-amendment 3 of the 17th then I would lean towards a C3.

If it was post amendment 3 then C2 as it should have been done properly when installed.
 
Could just be down to the RCD. Always find a difference in Zs before and after the RCD.
Measured one the other day 0.25ohms before the RCD, 0.85 ohms after the RCD resulting in a higher than expected Zs for the circuit.
 
How much higher is slightly higher?

If only slightly then you may find that the Zs is still within the maximum permitted values stated by the manufacturers' instructions / data.
 
0.1ohm is still likely in tolerance if you can alter the cmin factor a little.

Or look at manufacturer data for the MCB. BS7671 is sometimes overly cautious with the values it uses.
 

Reply to What if a circuits Max Zs is exceeded but the circuit is protected by an RCD? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope you get better soon .sounds quite serious
    • Friendly
    • Like
Replies
12
Views
757
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
806
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top