What is the name of the fault when main bonding high resistance? | on ElectriciansForums
Discuss What is the name of the fault when main bonding high resistance? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
N
nazoom
Hi
What do we call the type of fault when the main bonding conductor has high resistance higher than 0.05?
Is it called non-continuous? Or high impedance?
Many Thanks
Yes, The continuity of main bonding to water was higher than 0.05. About 2.2 ohm. And the length of cpc is not longer than 2 meters.
Several possible options here.
1/ Twist and pull the cable while doing the continuity test, if the value stays the same then its either a failed connection, non calibrated instrument. (press the calibration/zero button each time you do a low reading ohm measurement test)
2/ If the reading changes then the connection is loose or corroded. or the conductors within the cable are damaged, unlikely, but still....
Hi
Many Thanks
I would say High Resistance as your not testing with AC, your Low ohms meter is DC
Yes I checked and nulled out my tester. I just want to know the name of this fault so i can record it in the report.
Thanks.
Sounds like a high resistance fault( HRF) on a cable that should have a low resistance, you could refer to it as a or HRR (high resistance reading) or a HRROAC ( high resistance reading on a cable) or a TAHRROTCWSIPOTSFT (that's a high resistance reading on that cable what should I put on the sheet for that) lol
Thanks.
Equipotential bonding conductor to gas/water(delete as appropriate) has a resistance of X ohms,
Report done.
See that, I used my head for about 3 seconds and came up with something even a monkey could understand.
Reply to What is the name of the fault when main bonding high resistance? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
A lot of external bonding or earth conductors are bare copper strips. If mechanical damage is likely, then run some steel conduit… but all UV...