because it is C1 - no continuity on MPBC. The resistance over 2 ohms on MPBC the cable is f ... d and is not able to accomodate fault current flow into safety

- - - Updated - - -


i bet you make a fortune doing eicr and classing everything in site a C1

obviously someone shouldnt be doing EICR'S in here wink wink nudge nudge
 
konrad
C1 Danger present,immediate risk of injury


Without any means of earthing there will always be a potential danger,but it won't an be "immediate" risk of injury
A system can function for eons without an earth and the danger is always only potential

For it to be immediate there has to be direct risk at that moment,you can shove your fingers on a live bare conductor for instance,the earthing is very important but not a life threatening present condition
 
Yes, The continuity of main bonding to water was higher than 0.05. About 2.2 ohm. And the length of cpc is not longer than 2 meters.

Thanks

Just thought I'd better mention that there is no upper limit on main protective bonding conductor resistance values.....
Obviously the lower the better and in the scenario that you describe, there is certainly a fault but there is no 0.05 Ohm limit.
 
Just thought I'd better mention that there is no upper limit on main protective bonding conductor resistance values.....
Obviously the lower the better and in the scenario that you describe, there is certainly a fault but there is no 0.05 Ohm limit.

The firm I'm subbing to insist on 0.05, calculated from potential touch voltage, I have asked them to confirm this, and where the formula is and they go "a bit vague" on me....they tend to be a bit "monkey see...monkey do". Unless it's the supplementary bonding formula...415.2.2...
 
The firm I'm subbing to insist on 0.05, calculated from potential touch voltage, I have asked them to confirm this, and where the formula is and they go "a bit vague" on me....they tend to be a bit "monkey see...monkey do". Unless it's the supplementary bonding formula...415.2.2...

Yes, the passage reads like this:

This method can also be used to confirm a bonding connection between extraneous-conductive parts where it is not possible to see a bonding connection, e.g. where bonding
clamps have been ‘built in’. The test would be done by connecting the leads of the
instrument between any two points such as metallic pipes and looking for a low reading
of the order of 0.05 Ω

I've highlighted the key words-'between extraneous-conductive parts'
 
So, if it has no continuity how does the OP get a value of 2.2ohms? Surely it's just got a high resistance value but is still continuous?

as for Konrads rant, he lost me, when did this become a matter of surge protection?
 
So, if it has no continuity how does the OP get a value of 2.2ohms? Surely it's just got a high resistance value but is still continuous?

as for Konrads rant, he lost me, when did this become a matter of surge protection?

You're right-I'm not sure the OP was carrying out the test procedure correctly-if you have a MPB conductor length of 2 Metres as he states and a reading of 2.2 Ohms then surely the fault isn't too hard to find?
 

Reply to What is the name of the fault when main bonding high resistance? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
597
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
444
Hi all. Try to keep this nice and short. Had an EICR fail on a health centre due to corrosion on main supply which was causing high Ze values...
Replies
0
Views
210

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top