Cheers guys checked out the job. Anyhow x3 (3KW Dimplex heaters) were installed on a 2.5 T&E, covered by a 20A Type B MCB. Circuit even had an inter connection. One cable going off to feed 2 heaters and 1 going off the other way for the other one. So I am going to suggest re-wiring properly as a radial using 4mm T&E and sticking in a 40A MCB.
As previously stated a 40a mcb will exceed the rating of a 4.0mm T/E Their are no spare ways in the board so seems the only choice rather than seperate circuits for each heater. 9000watt comes to 39A so that protective device will cover it,
You will need to calculate volt drop and select a cable accordingly although I am wondering should it be an RCBO these days in commercial office blocks supplying fixed equipment or can I get away with a MCB and what type usually for these heaters B or C?
As long as not socket outlets,buried cables or a TT no requirement for RCD....no inrush current so a type B would cover, Would you believe I had my 17th