Here is what a rod should read and what our old friend E54 advocates.
Fair enough it is not a single rod but 15 19mm dia x 1800mm length rods in a network around the building all joined by a 70mm conductor. So a bit expensive and also would pay havoc in Mr Browns raised flower beds!!!
It is a functional earth for data and our remit was less than 1ohm, so pretty pleased with that