What Rods should read

M

malcolmsanford

IMG0225A.jpg

Here is what a rod should read and what our old friend E54 advocates.

Fair enough it is not a single rod but 15 19mm dia x 1800mm length rods in a network around the building all joined by a 70mm conductor. So a bit expensive and also would pay havoc in Mr Browns raised flower beds!!!

It is a functional earth for data and our remit was less than 1ohm, so pretty pleased with that
 
I can't really say too much as it is a military installation but Marvo is virtually spot on. The equipment is high tech IT equipment with an emphasis on...... struggling to know what to say but it's virtually an x box scenario but a little more realistic.

Put it this way the building has 7 data rooms with about 20+ racks each room all connected together to achieve the result. Unfortunately being an old sparks the data side of this and all the hardware/software is a little beyond me, but the spec was a 1 ohm "clean" earth or "noiseless" earth so it could not be go via the transformer.


The actual supply into the building is via 3 Tx and I'll show you the earth grid around that when it is finished. I was asked to help on that but fortunately we had some HV guys sort that part out
bassically it is a military spec server/supercomputer building.


i say server loosly because it sounds to me like a giant hpc cluster
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
malcolmsanford,
Last reply from
shanky887614,
Replies
30
Views
3,423

Advert

TrueNAS JBOD Storage Server

Back
Top