What test to carry out before consumer unit change? | on ElectriciansForums
Discuss What test to carry out before consumer unit change? in the UK Electrical Forum area at ElectriciansForums.net
Status
Not open for further replies.
London
What test should I carry out before changing a consumer unit to ensure that it is eligible for one?
I’m guessing R1 + R2 to make sure it has cpc at circuits. Say for lighting do I check every single light fitting or...?
IR test I’m assuming of course so there are no trips.
I’m not a testing qualified just installation. So this info will help me out for a CU coming up. I will be getting someone to test it and cert it afterwards.
Thanks for any help.
You can test at the furthest point if you can work out which it is , or I sometimes just do a bit of random testing at some of the more easy accessible points
As for IR , yes it is often wise to do some IR testing to avoid and tripping issues later
Thank you.
I forgot to mention end to ends for ring circuits. Do I need to do the figure of 8 test step 2&3 of ring continuity) too, or is this just for new installations for polarity check?
Are these test sufficient for a consumer unit change?
Remember the checks before a CU change are really about establishing what extra work is likely to be involved in making the installation safe & reliable overall. After the CU change you have all of the usual tests to be done anyway, but you really want to be able to quote the customer a realistic price first and explain why so they don't get a nasty surprise later and you get a reputation for not sticking to the expected quote.
So global IR (L+N to E) is a good and simple one:
  • If above a couple of Mohm at 500V all is fine
  • If not, but OK at 250V probably a SPD in some extension cable - not a big risk.
  • If a few tens of kOhm it might be a RCD socket outlet or similar, but it could be more trouble like soaked/trashed cable or wet junction box.
  • If few ohms or less then a N - E short that has to be found and fixed
Checking CPC continuity is another important point:
  • For any RFC the end-end loop R is a very good start, though does not prove any spurs are correct, but otherwise high confidence
  • For any radial a R1+R2 check at furthest point is good test (for radial sockets again not proving any other branches are OK)
  • Light circuits - always a worry as pre-1966 wiring might lack CPCs (see BPG#1 for info on that case) or sadly more likely is some muppet did not connect up CPCs thinking lights were double-insulated or similar. Again R1+R2 test or wander lead to a couple of light fittings will find if serious issue or not.
Checking the means of earthing / supply Ze is important so any assumptions on design values for final Zs, etc, are acceptable.
Last but by no means least, the danger of linked circuits:
  • The issue of a "borrowed neutral" between light circuits, typically a badly implemented up/down system. Not only dangerous but going to trip any RCBO/RCD.
  • A cross-linked pair of RFC (where two RFC are in one giant loop fed from two MCBs) which is a major safety risk as well since 64A equivalent breaker way above 2.5mm cable's safe ratings
Thank you.
I do end to end on all rings
I do IR tests where possible
and R1 R2 at easy positions
Ze
Zs
RCD trip times
personally don't bother with figure 8
Would you know and understand the results if you were told how and what tests to do?
Thank you for this very in depth answer!
I did some fault finding to try find a nuisance trip of the house which I will be changing the CU. I’ve narrowed it down to fridge freezer, fish tank filter or pump as I put them in an extension lead for the time being on a socket fed by the RCD that wasn’t tripping and it tripped same day.
It is currently a RCD split board installed by Mr bodger. I’ve recommend they get it redone and changed to RCBO board. They also use so many extensions. Every socket has a fully occupied extension lead minimum 4 plugs. Anyways I did IR test with everything unplugged and it was clear.
Will need to do R1 + R2 tests tho.
I did end to end and like you mentioned about the split ring being fed by 2x 32a MCB that’s exactly what I found. I also found another ring which had been split but this ring had one of its LNE leg just connector blocked floating inside the CU.
Can I just check the Ze or does Zs need to be carried out too before the CU change?
When finding out if there are borrowed neutrals, I’m guessing I would check continuity between neutral and other neutral conductors at the board. For example disconnect 1 neutral and test between that conductor and the neutral bars?
Yes I would. I learnt testing as part of my apprenticeship. If I don’t understand I would do some reading in the books or some research about it. I feel pretty confident but even so I’m hesitant sometimes and like to verify and gain further info from other more skilled and experienced electricians.
R1 + R2 I would get a reading if there is continuous cpc, would operate the light switch to get the reading and off to remove it. If I get no reading then there’s no continuous earth/ break somewhere.
IR test between conductors of say L to N would mean there is a short between them somewhere.
Having a current clamp meter that goes down to 1mA or so is useful here to find out if it is an accumulation of AC leakage from capacitance (so you see around 10mA-ish all the time) or a fault (usually near zero but something occasionally spike enough to trip it).
This is good value for that job (but like most affordable ones, AC-only):
Basically you clamp L&N of each circuit to see what is leaking. Clamping the CPC can give bizarre high readings due to parallel return paths in TN-C-S cases.
Probably too much on one RCD.
More sockets are always handy if there is space to fit them. Or at the very least having good quality extension blocks for the likes of TV/AV/Hi-Fi and IT stuff.
Olson Electronics (London based company) make really good metal cased ones, but at a price. We have some dating from 1991 still in good working condition!
OK, you know that well!
Ze (i.e. supply earth tested with installation off and it separated) is most fundamental as it is the only one you ought to rely upon for fault disconnection:
  • If TT it should be under 200 ohms, and definitely find and inspect the rod(s) it to see if in sound condition.
  • For TN supplies you would normally see under 0.8 ohm (TN-S) or 0.35 ohm (TN-C-S) but that is not guaranteed. Those TN values are used in the OSG for guidance on circuit size, etc.
Measuring Zs at the DB to get max PFC, and measuring max PSCC, is easier and the higher of the two tells you if the OCPD can safely disconnect, etc. But with modern domestic CU you are very unlikely to ever see an issue as they can disconnect to 6kA at least. Old rewirable can be a risk though, at 1kA or 2kA typical max PFC.
But checking Zs is not telling you Ze is good - it might be relying on service pipe bonding that can change externally and without warning due to repairs when metal pipes are replaced with plastic.
Typically you need to IR one circuit to another, and with two-way switches in all permutations, as typically it is L of one circuit returning via N of another so only in some positions is it connected, and it depends on the lamp (which could be LED or CFL) being driven in to conduction which might need tens of volts at least.
I think the ROI regs demand that circuit-circuit isolation is measured, basically this sort of test.
Sorry for not quoting your message properly I’m not too familiar with how to use this on mobile.
That’s quite a cheap current clamp meter, thanks for linking me that will have to buy it.
Yeah I thought it would be too much on one RCD too, thats why I thought I’d suggest them the RCBO board.
Okay thanks for the info on the Ze Zs. The intake is a TN-S as it’s earth of the armoured outer sheath. Hopefully the Ze is good as they haven’t even got any bonding to water or gas. Will have to install these before I even start on the CU stuff.
So for the borrowed neutral I would need to IR test L from one circuit to N of other circuits let’s say upstairs lighting L and downstairs lighting N? If there is a lamp in and the switches are operated on off on off and I get a reading it will give me a low reading as it’s passing through L and passing through the lamp back through N?
You lost me when you mentioned I would need tens of volts at least?
In theory wouldn’t the continuity method between one circuits neutral and another circuits neutral give me an idea too if there is a borrowed neutral as well as the IR test?
Thank you 😀
Ze
Zs
RCD trip times
This is exactly the best way to think about testing just simplify it without overcomplicating matters. Providing you know the max permissible values or know where to find them then it’s all straight forward
Reading #7, this could be an absolute mare of a job.
You’re going to find all sorts.
Depending on how bodgy it’s been, and age of propert, expect incomplete rings, no cpc between downlights, no earth link to metal accessories, attic jointboxes without lids….
I actually wouldn’t do this, I’d stick to L+N to E for IR tests. That is basically pat testing the entire house at once and it isn’t uncommon to have to go around and unplug things to find the item that is on its way out / the last one I did was an oven on a plug top.
Any other IR test permutation or between circuits risks damage to connected equipment.
Yes in my view continuity is enough.
You are basically after big picture tests to give you the general idea before a CU change.
Status
Reply to What test to carry out before consumer unit change? in the UK Electrical Forum area at ElectriciansForums.net
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
The last couple of de-loops that I have been involved with had the single phase supply replaced with a three phase cutout (as I believe the DNOs...