Lol, that ESC just can't get anything right.
Just noticed this: "Absence of RCD protection for portable or mobile equipment that may reasonably be expected to be used outdoors"
I wonder which Regulation that relates to?
 
Lol, that ESC just can't get anything right.
Just noticed this: "Absence of RCD protection for portable or mobile equipment that may reasonably be expected to be used outdoors"
I wonder which Regulation that relates to?
411.3.3 says mobile equipment with a current rating not exceeding 32A for use outdoors.

Definition of mobile equipment (portable equipment (deprecated)). Electrical equipment which is moved while in operation or which can easily be moved from one place to another while connected to the supply.

So your carrying out an inspection on a premises and none of the socket circuits have additional protection by means of a 30mA RCD.....You look at the mobile equipment that's likely to be used outdoors like a jet wash, vacuum etc and non have an RCD plug top or not an RCD adaptor in sight so you speak to who ever is in charge or the person who uses the mobile equipment outside and they confirm your findings that the mobile equipment just gets plugged in to the socket with no additional protection.. What do you code this?
 
411.3.3 says mobile equipment with a current rating not exceeding 32A for use outdoors.

Definition of mobile equipment (portable equipment (deprecated)). Electrical equipment which is moved while in operation or which can easily be moved from one place to another while connected to the supply.

So your carrying out an inspection on a premises and none of the socket circuits have additional protection by means of a 30mA RCD.....You look at the mobile equipment that's likely to be used outdoors like a jet wash, vacuum etc and non have an RCD plug top or not an RCD adaptor in sight so you speak to who ever is in charge or the person who uses the mobile equipment outside and they confirm your findings that the mobile equipment just gets plugged in to the socket with no additional protection.. What do you code this?
He is just checking the ESC recommendations.
 
That would be a code C2 as per BS7671 Regulation 411.3.3.
It would not be a code C2 as per some cobbled together regulation made up from a current and a 10 year odd old Regulation.
 
As it happens, I do agree with most of the ESC recommendations.
What I don't like is when they make no recommendation for non RCD protected circuits of locations containing baths or showers, or when they make up these other so called regulations.
 
I see you no longer have a reference to being registered with the NICEIC.
That's because the signatures have been removed as far as I am aware.

For the avoidance of doubt I am still an NICEIC Approved Contractor and a RECI Registered Electrical Contractor.
 
Seems I am incorrect.
They do not recommend a code C2, no code at all.
It is specifically stated that anywhere where an RCD is now required for additional protection cannot attract no code. It must at a minimum be given a C3. This comes straight from BS7671.
 
Anyway regs aside our job is to keep people safe. I and the OP merely asked for opinions on class codes on RCD's of not just one person but hopefully a more rounded fuller contribution on this matter. We need to communicate to the client any area we consider could be improved. The codes are one means of doing this. Hence the hope of pragmatic discussion as opposed to sniping at contributors. Clearly this is a grey area that needs some more definition/guidance. I do not wish to guide a client toward needless work but to a safer place to work or live in. All opinions welcomed! I want intelligent discussion on this matter not vacuous LOL blah blah blah. I see your not NICEIC, that is plainly not helping the Discussion to go forward.
 
No I'm not, I'm IET and JIB, though how that prevents a discussion from moving forward, I don't know.
Still you have Risteard who can discuss how the IET want a minimum code C3, but the NICEIC, no code at all.
 

Reply to what to suggest when no circuits have rcd protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
444
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
354
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
707

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top