Hi there,

I have a customer (I'm in IT, not an electrician, and am just getting information at this stage before appointing a contractor early next year) who is planning on having fibre and a switch in a couple of fields for events. We will be providing an IP65 cabinet with mains power, a fibre patch panel and a single 48 port network switch. The power requirement is just for one switch and the fans in the cabinet, and will only be powered for the duration of event prep, during the event and on take-down.

We'll be using a cabinet with 19 inch rails for the fibre patch and switch, and a separate locked section for the mains ingress, which event organisers would not have access to. The switch socket will be in this locked section.

The runs will be in a trench and could be as long as 600m. The source is a large (huge) house with a big distribution board.

My question is, for a low power requirement, but with the length of run, what size cable would be best, and do we need to consider inspection points and/or joints? There will be up to 4 of these trenches to different areas of the site, but they may only use one at a time depending on the size of the event.

Also, is it bad to go direct from point A to point B if it involves crossing a field which may have LGVs crossing for event setup and take-down, should the trench go around the perimeter?

Thanks very much

Mike
 
Doh! Table had 480V not 460V for the split-phase set up. Try again:

CSA \ Volts​
230​
400​
460​
630​
800​
ÂŁ/m​
For 600m​
2.5​
1​
3.0​
4.0​
7.5​
12.1​
ÂŁ0.95​
ÂŁ570.00​
4​
1.6​
4.8​
6.4​
12.0​
19.4​
ÂŁ1.25​
ÂŁ750.00​
6​
2.4​
7.3​
9.6​
18.0​
29.0​
ÂŁ1.80​
ÂŁ1,080.00​
10​
4​
12.1​
16.0​
30.0​
48.4​
ÂŁ2.42​
ÂŁ1,452.00​
16​
6.4​
19.4​
25.6​
48.0​
77.4​
ÂŁ3.73​
ÂŁ2,238.00​
25​
10​
30.2​
40.0​
75.0​
121.0​
ÂŁ5.75​
ÂŁ3,450.00​
 
Remember @pc1966 the volt drop can be bigger than 5%
if you set up the transformers correctly so you have maximum allowed voltage when at zero load, you will have to drop a lot before coming out of the nominal allowed range.
 
If all you need to power is some fixed equipment in a cabinet, rather than worrying about a 5% or whatever voltage drop, can you perhaps not just install a power conditioner / voltage stablizer?

These seem to exist from quite small loads e.g. 3A to 10A or 20A at quite reasonable costs ÂŁ100 to ÂŁ300. A typical input range might be 140-260V, with a 230V output +/- 6%. You might even find one that operates from 100V or less up to 260V or more, a bit like many AC adapters that work off both 110V and 230V.

Obviously this is not going to be some BS7671-compliant supply, but perhaps you treat the whole cabinet & very long supply cable as a fixed load from wherever it is supplied from?

But feel free to tell me this is a daft idea!
 
If all you need to power is some fixed equipment in a cabinet, rather than worrying about a 5% or whatever voltage drop, can you perhaps not just install a power conditioner / voltage stablizer?

These seem to exist from quite small loads e.g. 3A to 10A or 20A at quite reasonable costs ÂŁ100 to ÂŁ300. A typical input range might be 140-260V, with a 230V output +/- 6%. You might even find one that operates from 100V or less up to 260V or more, a bit like many AC adapters that work off both 110V and 230V.
It is a very good suggestion. In fact, many IT systems would be planned to include a UPS and usually they will 'condition' the normal input range to come out at a since stable 230V.

Not all UPS are very well behaved in this, the expensive double-conversion sort (continuously converting incoming AC to the DC battery bus, and back to stable AC again) are good, but typically if you dip below nominal input the revert to battery operations.

I can see an oscillating cycle in the case of a high Z supply where it reverts to battery, AC demand goes to zero, volts recover, ...
Obviously this is not going to be some BS7671-compliant supply, but perhaps you treat the whole cabinet & very long supply cable as a fixed load from wherever it is supplied from?

But feel free to tell me this is a daft idea!
Here would be a reasonable case for a departure from BS7671 as it has no safety implications (high cable drop not related to exceeding the CCC) provided the design of RCD/OCPD is such that disconnection under fault conditions is still met.
 
Looking briefly for transformers, if the house has 3-phase so you can have L1 & L2 on the feed for 400V, then this at the far end would give to 4A 230V out with 4mm feed cable:
So then cost around ÂŁ1k, plus any extra for enclosure and added RCD on transformer output (with the pre-RCD neutral to the supply cable armour for earth referencing).

Supply OCPD is probably a DP/3P MCB and it is unlikely to meet disconnection times, so possibly added cost of a 3-phase RCD as well.
 
It seems a bit vague: power for networking, but not anything else?

So maybe the customer needs to think this through much more and plan on remote power from generator/solar+battery/etc so only fibre ducted through, or look at biting the bullet and putting in a usable amount of power.

Which IS going to cost a lot, even if tricks with transformers and UPS are considered.
 

Reply to What type and size of cable for a long underground run in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
937
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top