Hi there,
I have a customer (I'm in IT, not an electrician, and am just getting information at this stage before appointing a contractor early next year) who is planning on having fibre and a switch in a couple of fields for events. We will be providing an IP65 cabinet with mains power, a fibre patch panel and a single 48 port network switch. The power requirement is just for one switch and the fans in the cabinet, and will only be powered for the duration of event prep, during the event and on take-down.
We'll be using a cabinet with 19 inch rails for the fibre patch and switch, and a separate locked section for the mains ingress, which event organisers would not have access to. The switch socket will be in this locked section.
The runs will be in a trench and could be as long as 600m. The source is a large (huge) house with a big distribution board.
My question is, for a low power requirement, but with the length of run, what size cable would be best, and do we need to consider inspection points and/or joints? There will be up to 4 of these trenches to different areas of the site, but they may only use one at a time depending on the size of the event.
Also, is it bad to go direct from point A to point B if it involves crossing a field which may have LGVs crossing for event setup and take-down, should the trench go around the perimeter?
Thanks very much
Mike
To give some idea - a 3 amp load (guess) and a 600m run works out at 10mm sq. SWA just to keep the volt drop under the 5% requirement. 5 amps would push it up to 16mm sq.
Have you thought about other options?
It may be worth asking the question how many events there are a year that would use this and whether a small genny is a viable option.
Or even charge up a UPS before the event - I'd imagine a modest UPS would keep that load alive for at least a couple of weeks.
Or even charge up a UPS before the event - I'd imagine a modest £100 UPS would keep that load alive for at least a couple of weeks.
Thanks for the reply. We're having to trench fibre to each location so at the time made sense to run power lower down. Generators are most likely going to be ruled out by the home owner. A UPS could be a consideration but event organisers will be paying for the service and there are planned to be upwards of 8 major events each year lasting from 1 to 5 days.
I was aiming for a 5a load. I think if the cost is prohibitive then at worst we'd just run the fibre and let the organisers figure it out from there. That gives me some notion of cable size, and thanks for the other considerations.
Large house, if there is 3 phase available it may be worth looking at using 2 phases into a transformer with a 2:1 ratio.
this will give aprox 800v for the distribution run
this will reduce the current in the cable to less than 1/3 of what it would be at 230v
a transformer at the other end (in the cabinet) to bring 800v down to 230v
with a 600m run, the cost of the transformers should be offset by the lower cost of the smaller cable required.
volt drop is unlikey to be an issue as you will
a. be able to modify the voltage to acceptable values by altering the tapping's on the transformers.
b. not be a great issue in practice because most I.T equipment will happily run at a voltage range from 100 to 240v
A 48 port switch - simple one is around 25watts, Fibre converters again only a few watts, as for fans, do you really need them ? - So consumption in amps at 240V is tiny a few hundred milli amps.
When you price up the cable at that distance and then the cost of installation, batteries will appear very attractive.......
You can afford to reduce the size of the cable for that load but beware terminating with a general purpose socket to plug in the switch as it will be too attractive for anybody wanting to use it for a lawnmower, lol
Thanks. I think there is 3 phase, will need to check. I think even with having to dig a trench, the cost of electrical cabling will make them think again!
Thanks. Yes, batteries may well be the way forward!
1.5mm 2 core SWA is £1 per meter
if you can deal with the volt drop by using a transformer or 2
the maximum load you could support using 800v transmission voltage is about 16Kw
however, i would think that specifying for a 1000w (1.25A @ 800v) load would be more realistic, just in case you want a 250W anti frost heater inside the coms rack.
Realistically if you are looking at just a switch and maybe a small defrost heater then 1A / 230V is enough and you could use 2.5mm 2-core SWA with an RCD for supply disconnection (as it would fail on the typical min 6A OCPD for domestic style boards). If the house is PME supply and you are looking at outdoor stuff you might even want to make this a TT arrangement.
Using transformers for lower drop as @James suggests is possible, but I would suggest unnecessary complexity if you don't really need it.
Cable works out at about £1/m plus VAT.:
You can either use SWA network cable and both can be buried directly in the ground but I would strongly advice using some twinwall duct for both power and fibre and you can use any outdoor style fibre that is strong enough to be pulled through. Mains SWA is safe enough beside even normal copper network cable as it has an earthed screen in the form of the armour. This is the sort of thing (but shop around, this was just my first result that was what I was trying to illustrate) so around £1.60 per meter plus VAT:
Typically you would want an access chamber around every 200m to allow cable pulling and potentially to allow a section to be repaired. It also allows you to have one run out and then split at the box to serve other end points.
BT/Openreach typically use this system for pavements or footpaths (not on a road where heavy concrete or cast iron cover and a concrete or brick box is then needed for the loading):
However, you can see that a complete box (say 4 * stacked sections to get 60cm depth, and lid) you are looking at around £600 per box.
So for 600m run you are looking at around 4 grand for duct, 3 boxs, and SWA cable delivering 1A power (before you add fibre and network switch). However, if fibre is needed out there then most of that cost is going to apply anyway.
If the cable or duct is buried deep enough (say 0.4-0.5m below surface) then it is not important. However, if the field is ever used for agriculture then you really need around 1-1.2m depth.
If this was a permanent system then you might want it routed around the edge of fields to allow for future changes in land use (e.g. adding building) without having to change this, however, that might not be an issue for the owner here.
comclusive,
Mikegh,