Hi,
Just a quick question i was thinking about today. Say if your measured ze was over the maximum value. Say for arguments sake a tncs was 0.5ohms.
Would

1) It be fine leaving it as this value aslong as all circuits fall within maximum Zs
or
2) Install an earth rod and make the installation TT, as with the ze being over the maximum value it can not be classed as a stable earth???

Aint got the regs to hand to check if theres anything in on this, and just wondered what peoples view on this would be
 
If a pme system had a reading that high, I would say further investigation would be neccassary to establish if there is an underlying problem with the dno's supply.
So inform them accordingly.
An RCD would sort the problem, but what if the integrity of the earth is degrading over time and your Ze is getting higher and higher.
 
be certain of your reading, then contact DNO. just fitting a RCD is like putting a plaster on a severed leg. treat the cause, not the symptom.
 
Last edited:
Make sure you have a high current Ze reading (not no-trip), if the out of range reading confirmed, isolate the installation (you should have done this before measuring Ze of course) if you haven't already, phone the DNO immediately, this will be logged as a priority event and they will send a linesman to you (in my area within 1 hour, amazing in a rural county without motorways) to investigate and fix fault. Your TN-C-S installation is connected to a chain of protective multiple earth points (PME) and your high reading indicates a latent fault in this chain. Remember your property will amongst a number in the area connected to this network and thus potentially at risk, hence the priority for the DNO act.
 
Last edited by a moderator:
Hi,
Just a quick question i was thinking about today. Say if your measured ze was over the maximum value. Say for arguments sake a tncs was 0.5ohms.
Would

1) It be fine leaving it as this value aslong as all circuits fall within maximum Zs
or
2) Install an earth rod and make the installation TT, as with the ze being over the maximum value it can not be classed as a stable earth???

Aint got the regs to hand to check if theres anything in on this, and just wondered what peoples view on this would be

All sound advice about contacting the DNO and making sure you have the correct reading. But to be honest a 0.15 overeading is not going to make the DNO loose sleep over this as they know that our MFT are not that accurate, but they will check it saying that.

Oh and if the Zs is within range why are we fitting all these RCD/RCBOs
 
Cheers guys! The tncs was just an example. It was just a general wondering I had that's all, and just thought id ask to see what people would do I they came across it.
 
Also worth remembering that with the nuetral and protective conductors sharing a common return path in this way. A load no load check on the voltage supply would also be worth while. It may well be that its not just the Ze thats going to be affected.
 
not sure on that statement my understanding is max Ze values are in place regardless of what size suppliers fuse is, the stated values would give a minimum fault current that that can be safely handled.
 

Reply to What would you do?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
786
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Thanks I re tested this morning as I had other bits to finish off . I tested three times and it was 0.30 every time . It may have been my leads...
Replies
7
Views
2K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top