Interesting? The higher the fuse rating the lower the Ze for a given disconnection time. The relationship between Ze and cutout fuse size is to ensure a disconnection time of 5 seconds for a fault between the cutout fuse and the consumers installation, The figures for max Ze quoted by my DNO (revised due to decared voltage change to 230V) are :
These figures are very close to table 41.4 in the regs for a BS1361 fuse 5 second disconnection time. FYI These Max values quoted are measured at the cutout with the customers earth disconnected not the consumers installation. I hope this makes sense.