There is no relation to max Ze TNC-S of 0.35ohms to the cut out fuse values... It is considered to remain the same value regardless!!

Interesting? The higher the fuse rating the lower the Ze for a given disconnection time. The relationship between Ze and cutout fuse size is to ensure a disconnection time of 5 seconds for a fault between the cutout fuse and the consumers installation, The figures for max Ze quoted by my DNO (revised due to decared voltage change to 230V) are :

100A = 0.38ohms
80A = 0.52ohms
60A = 0.73ohms
45A = 1 ohm

These figures are very close to table 41.4 in the regs for a BS1361 fuse 5 second disconnection time. FYI These Max values quoted are measured at the cutout with the customers earth disconnected not the consumers installation. I hope this makes sense.
 

Reply to What would you do?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Thanks I re tested this morning as I had other bits to finish off . I tested three times and it was 0.30 every time . It may have been my leads...
Replies
7
Views
2K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top