What’s the going rates for the below instalation | on ElectriciansForums

Discuss What’s the going rates for the below instalation in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 1, 2019
Messages
9
Reaction score
0
Location
London
Hi just starting out working for my self after 10 years on the rail and I’m at a total loss at what the going rates are I don’t want to go in to high .I have been asked price up to Run a supply to a Bar in a garden, but due to the location of the distribution board in the house It would be easier to install a enclosure next to the meter And split the meter tails . The run is 35m to the bar so I was going to install a 6mm SWA cable protected by a 50amp 100m/a RCBO then install a 4 way DB with a 40amp 30m/a RCD mainswitch in the bar with a 20amp radial with 5 x double sockets 1 x lighting circuit. Any advice would be greatly appreciated
 
Why are you sizing cable for 50A capacity?? Ib for distribution circuit .....approx 22A

1. 20A for socket outlets as could be fully loaded so base on MCB,
2. Say.......2A for lighting

Protective device only needs to be equal or greater than design current ....

16mm for a 22A Ib 35M away.......No! :)

6mm is more than enough for CCC and VD. Zs for ADS you can work out as I don't know your Ze.

As already said don't RCD front end. 30mA Main Switch RCD in sub board. Put B40A on dist circuit as it is the highest you can go and will discriminate better with the B20 in sub board on SC'S.
 
Why are you sizing cable for 50A capacity?? Ib for distribution circuit .....approx 22A

1. 20A for socket outlets as could be fully loaded so base on MCB,
2. Say.......2A for lighting

Protective device only needs to be equal or greater than design current ....

16mm for a 22A Ib 35M away.......No! :)

6mm is more than enough for CCC and VD. Zs for ADS you can work out as I don't know your Ze.

As already said don't RCD front end. 30mA Main Switch RCD in sub board. Put B40A on dist circuit as it is the highest you can go and will discriminate better with the B20 in sub board on SC'S.
Hi TJ thanks
 

Reply to What’s the going rates for the below instalation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top