When do Neutrals need to be switched?
Sorry if this is a silly question but I can’t get an answer from colleagues as it’s a “I dunno”. So I thought I’d ask here!
Some of our TPN DB’s have a 3 pole main switch with a block for the neutral. Other TPN DB’s we have here have a 4 pole main switch which switches the neutral.
It’s the same for our machine isolators. Some have a 4 pole rotary switch and others have a 3 pole rotary switch with a connector block for the neutrals.
When do we need to switch neutrals & why?
Apologies again if it’s a silly question or something I should already know. I’d like to learn.
Thanks guys.
Neutral is a "live" conductor so should generally be switched
Also even with TN where the neutral is reliably at earth potential it can be safer to switch
If the OP is talking about 3 phase, then the N is normally solid linked.
If the Neutral is switched, then the 4 pole switch should be late disconnect and early make.
Id disagree, if a neutral hangs and single phase circuits connected in a TPN board then 400 volts can go across 230 volt connected equipment, seen it happen and generally as mentioned by Risteard can be hazardous
Hence, the need for late break early make isolator.
Bathroom fan?
Nothing wrong with having a 4 pole local isolator near the fan, but if single phase equipment is connected to a three phase board I would not switch the main neutral at the incoming DB switch, this is a discussion which could get quite intense if several sparks started debating it lol, however when you have seen a hung neutral like I have then you would not switch a neutral on single phase circuits if connected to 400 volt distribution.
MaintenanceSpark,
Marvo,
TrueNAS JBOD Storage Server
