When do Neutrals need to be switched? | on ElectriciansForums
Discuss When do Neutrals need to be switched? in the UK Electrical Forum area at ElectriciansForums.net
Worcestershire
Sorry if this is a silly question but I can’t get an answer from colleagues as it’s a “I dunno”. So I thought I’d ask here!
Some of our TPN DB’s have a 3 pole main switch with a block for the neutral. Other TPN DB’s we have here have a 4 pole main switch which switches the neutral.
It’s the same for our machine isolators. Some have a 4 pole rotary switch and others have a 3 pole rotary switch with a connector block for the neutrals.
When do we need to switch neutrals & why?
Apologies again if it’s a silly question or something I should already know. I’d like to learn.
Thanks guys.
Neutral is a "live" conductor so should generally be switched
Also even with TN where the neutral is reliably at earth potential it can be safer to switch
If the OP is talking about 3 phase, then the N is normally solid linked.
If the Neutral is switched, then the 4 pole switch should be late disconnect and early make.
Indeed. It can be more hazardous to break the neutral in this scenario.
Id disagree, if a neutral hangs and single phase circuits connected in a TPN board then 400 volts can go across 230 volt connected equipment, seen it happen and generally as mentioned by Risteard can be hazardous
Hence, the need for late break early make isolator.
Bathroom fan?
Nothing wrong with having a 4 pole local isolator near the fan, but if single phase equipment is connected to a three phase board I would not switch the main neutral at the incoming DB switch, this is a discussion which could get quite intense if several sparks started debating it lol, however when you have seen a hung neutral like I have then you would not switch a neutral on single phase circuits if connected to 400 volt distribution.
Our local regs (not UK) require both L+N to be switched if earthing arrangement is TT.
Hi Mate, hows the old legs?
Reply to When do Neutrals need to be switched? in the UK Electrical Forum area at ElectriciansForums.net
Not sure if I’ve understood this properly, but it appears to have parallels with my own installation. I highly dislike the idea of feeding SP...
5K
Noted. Thank you. Out of phase summation being the answer to the question.
Thank you, what would be the advice for me to do in this scenario? I've also seen circuits tripped in past from other things such as 1500VA step...
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
N
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...