When is a Ring NOT a ring? | on ElectriciansForums

Discuss When is a Ring NOT a ring? in the Australia area at ElectriciansForums.net

1

1shortcircuit

When some flipping ruddy IDIOT leaves one leg half way up the length of trunking because it wouldn't reach the socket!

I sh*t you not! I've been on this last job two days and I was only sent to add a spur for a washing machine.

Checked the gas and water bonding and all was well.

Circuit protected by 32amp RCBO so all well there too.

Tested end to end for continuity.... Doh!


First observation was that the house had been wired Front and Back rings as opposed to up down which threw me off track on day one. Today though I approached with a fresh head and quickly realised what was going on.

Only one thing wasn't adding up whilst I was testing between all the sockets and that was "WHY" when rewiring a house would someone just run a spur to one double socket in one of the bedrooms? There was no sign of where the spur had come from either? I guessed there must be a junction box somewhere?

I went in search and lucky for me all of the upstairs had no carpets. First board I lifted and hey presto... WTF! I spotted that there were actually two cables heading in the direction of the spurred socket... Um! This was never intended to be a spur... I could not believe that the second leg had been poked up behind the skirting board and JUST made it in to the trunking. There was NO SLACK on the cables so my only conclusion is that this circuit has NEVER been anything other than two radials on a 32amp RCBO with live conductors hidden behind the trunking :yikes


I am so pleased with myself for doing the initial checks before commencing the work that I had been sent in to do.

Just for the record, this was a council property and had recently (last two years) undergone a full rewire which I presume would have had to have been carried out by an NICEIC approved contractor?

This has just emphasised how important it is to test a circuit before commencing work. I know some of you more experienced would have learnt this a long long time ago and I've read posts explaining the same on here but when you actually do AND find a fault it makes it so much more satisfying.

Thanks for reading all:thumbsup
 
Good work!
I was testing a lot of council rewire jobs a couple of years back and the company I worked for had their annual NICEIC inspection. We chose a nice easy house for access and made sure everything was complete. The NICEIC inspector had the test results I had measured immediately after the rewire and asked me to test the ground floor general ring main. I have never been so embarrased to find no ring continuity on any of the conductors. My boss was a little red faced and had a few questions for me especially as I hads tested a 2-300 propertys and this the first he checked with me.

Turned out in the 6 days between the test and the niceic coming down, her grandson had installed a couple more sockets for her and left the ring open circuit. Surprisingly the NICEIC chap was fine about it and gave us a good report.
 
Last edited by a moderator:
I agree with Mark, you should give the tenant a report and a seperate invoice for the repair only. They can then complain to their Landlord and attempt to recover the cost of the repair.

It's a Council owned property and was rewired by the Council too, now that it has been corrected I'm pretty sure they probably won't give a monkey's?

Also, from what I've seen discussed regarding the NICEIC that would probably be a worthless shout also?

My job is done and the property is safe, I can sleep well in my bed this evening knowing this :thumbsup
 

Reply to When is a Ring NOT a ring? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
594
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Yep! Edit button was disabled by the time I seen it. Hopefully the 15m/15m clarified what I intended 😀
2 3
Replies
36
Views
2K
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top