Sorry in advance for what may be a daft student question. Where should I measure my Ze? My mum has a TNCS system with the meter/incoming supply at one end of her bungalow. The CU is some distance away (I guess around 15m) and connected via T&E. Do I attempt to measure Ze at the incoming or at the CU. There is no obvious place at the meter to take a reading easily. On my course we always do it in the consumer unit but of course that's not real life.

I'm just wondering what size this bit of T&E is ....... and how big is the fuse "protecting" it.
 
I would put a BS88 fuse instead of the isolator as it will give a higher maximum Zs. Also it the T&E running through thermal insulation as this greatly reduces the current rating of the cable. All of this should be taken in consideration when deciding the size of the fuse. For a TNCS system the minimum size of your earth cable should be 10mm.
 
First thoughts Has the CU been moved at an earlier date ?
With 100A main fuse the meter tails should be 25 sqmm are they ?
What size is the T&E feeding the CU ?
Where is the MET ?
What size is the earthing conductor to the MET ?
Where are the protective bonding conductors terminated ?
What size are the tails from the meter to the isolator ?
How many ways on the CU ?
What is the estimated maximum demand ?
 

Reply to Where to measure Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
764
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
Replies
13
Views
784

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top