devlin maguire

Hi All
PNB system, I,v been told by the supply company" its not a PME system," I have had to sink three extra rods to the seperate buildings on this farm to get good disconnection times does that make it TT ? I mean can you turn a PNB system into a TT at all, is it not a TT to start with as the company Earth is within the proximity of the pole mounted transformer, DNO are being very vauge about this
Mac
 
Last edited by a moderator:
Hi All
PNB system, I,v been told by the supply company" its not a PME system," I have had to sink three extra rods to the seperate buildings on this farm to get good disconnection times does that make it TT ? I mean can you turn a PNB system into a TT at all, is it not a TT to start with as the company Earth is within the proximity of the pole mounted transformer, DNO are being very vauge about this
Mac

If there is no appreciable network between the pt and the service head it can not be pme, if its pnb there will be an earth electrode installed by the dno at the service head, any supply can be made tt simply by not making an earth connection to the dno service, install an installation electrode and rcd`s and thats it , the pt will be neutral referenced to earth at the pole

I would not entertain pme or pnb even if available for farm buildings especially if the buildings are housing livestock
 
Hi Guys and thanks, some info I did not include there is no suppliers earth at all this is because the supply goes to a all metal barn, the customer is required to provide his own earth electrode, so it's more or less sorted now. I will have to reference this in the BRB I seem to remember something along the lines of livestock and areas of shock risk with TT systems in agri property, anyone?
Mac
 

Reply to which box in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top