I do, you dont!
Discuss Whilst we're on the subject of bonding... in the Talk Electrician area at ElectriciansForums.net
Well im affraid sir your very wrong!
If in doubt then insulation test at 500v from MET to part in question <22k ohms bond if not NO NEED! If an installer wanted to he can nothing in bs7671 to say you cant!
But you may make the installation more dangerous if you bond unnecessarily. Daz
Would you care to elaborate on that??
1) i wouldnt say that two metallic parts that are 1666 ohms apart are at substantially the same potential, despite our interpretation of reg 415.2.2
2)Thats what i don't understand; - having 1666 ohms between an exposed conductive part and an extraneous conductive part during fault conditions will give a voltage approaching mains - depending on the circuit impedance of course.
cheers
sam
Absolutely not.. Diferent ph levels and salts in water can make it more or less conductive according to levels.. What is stopping the water board putting conductive pipe joint underground and then this becoming extraneous conductive.. Small copper pipe after stop tap earth to MET no PD between earths in installation, tick jobs a good one!
You are effectively making whatever it is that you have bonded a part of the electrical installation. For example, a metal sink - this cannot introduce a potential (even earth potential), and so is not extraneous and should not be bonded. You would not be making things safer by bonding it.
What would you be giving it a PD too, as everything that introduces a earth path must be bonded!!
Thanks, my statement wasn't factual. However, water is more conductive than fresh air, hence the precautions taken in special locations.Actually, water does not conduct electricity contrary to popular belief.
You don't.
If conditions are as described in reg 528.3.4, then '(ii) fault protection shall be afforded in accordance with the requirements of Section 411.'
Then bonding of metal pipes with plastic service supply, may be required.
You are effectively making whatever it is that you have bonded a part of the electrical installation. For example, a metal sink - this cannot introduce a potential (even earth potential), and so is not extraneous and should not be bonded. You would not be making things safer by bonding it.
What would you be giving it a PD too, as everything that introduces a earth path must be bonded!!
what if the metal sink has a metal waste, going into the ground?
Will it need a soakaway?what if the metal sink has a metal waste, going into the ground?
Hmmmm, that must be the problem then. I ain't got no multi quote button. Note to oneself, switch to Chrome.click the multi quote button at the bottom of every post you wish to reply to and then click on reply with quote.