Re-called to a job today.
(Hate it when that happens)
Motor overloads tripping on a 3ph. water pressure boost pump, but intermittently, not every day.

First visit, tested everything - current draw, voltage, winding resistances, IR etc - nothing,
no trips, everything working fine, like your car when you take it into the garage 'cos its running rough and then it purrs like a kitten, the swine ( the car, not you TC)
Put it down to the pump struggling to force water round the system, because it's a big house, and turned the O/L's up a bit - see how that goes.

Anyway, today its a bit different, clamped it and the current is fluctuating from 4+ to 6+ Amps, the pitch of the motor changed at the same time, sounds like it's losing a phase so checked it from that angle. turns out one of the line connections between the contactor and the O/L unit is burned and losing contact. cleaned it up, OK now, must have been a loose connection.

The pump/motor set including the base plate, Pressure switch, enclosure with MCB, RCD, Contactor and overloads was supplied and installed by the plumbers as a pre-wired unit, all I had to do at the time was to run a supply to it.

When I explained to my customer what the problem was, he said, didn't you check all the connections were tight when you installed it? Ouch, well yes, all the connections I made were tight, but this unit was supplied by others, quality control stickers on it, so would I be expected to go through someone else's work and check it?

Nevertheless his question stung a little, feel I should have spotted it first time, spent two apprentice weeks every Manchester Wakes tightening dist. board connections on shutdown planned maintenance.

So what do you all think, should we check connections made in supplied equipment? I normally check light fittings etc. but a whole panel? not charged him yet and not sure if I should.
 
Last edited:
You could always offer to check installed systems with a FLIR camera as an extra service when you install and charge accordingly.

[ElectriciansForums.net] Who's Fault?
 
You could always offer to check installed systems with a FLIR camera as an extra service when you install and charge accordingly.

View attachment 13331

Not a bad idea at all, certainly would have caught this problem, This guy has just spent €1.2 Mil upgrading his house (not with me) so cost shouldn't be a problem lol.
 

Reply to Who's Fault? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
374
  • Question
What @Avo Mk8 suggests crossed my mind. Try an IR test at 500v.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top