From the link above it shows total load rating as 7350w, which does not include the boost, presumably as it's only short term and you're unlikely to boost all 4 zones at the same time
Thanks Snowhead. Out of curiosity if you had a 3.2kw oven and 6.4kw hob would you have any issue with putting both on a 6mm? Have checked diversity equation in onsite guide and this seems to suggest would be ok but I am surprised at how much allowance this gives as all hobs and oven could potentially be on full power at the same time
 
Thanks Snowhead. Out of curiosity if you had a 3.2kw oven and 6.4kw hob would you have any issue with putting both on a 6mm? Have checked diversity equation in onsite guide and this seems to suggest would be ok but I am surprised at how much allowance this gives as all hobs and oven could potentially be on full power at the same time
they could all be switchred on, but the stats. will cycle them on/off at different times.
 
they could all be switchred on, but the stats. will cycle them on/off at different times.

Thanks Telectrix. So your comfortable using the diversity calcs out of onsite guide? Still pretty new in with doing my own works. Have another job coming up and hob and oven would be combined 11KW. Would probably be easier to put them both on a 6mm but other option is the oven tapped of ring. What do you generally do?
 
Thanks Telectrix. So your comfortable using the diversity calcs out of onsite guide? Still pretty new in with doing my own works. Have another job coming up and hob and oven would be combined 11KW. Would probably be easier to put them both on a 6mm but other option is the oven tapped of ring. What do you generally do?
Putting large loads on the ring is not a good idea!

If you are reaching the limit for already present radial circuit then options such as replacing with heavier wire or running a 2nd circuit are obvious better choices. 11kW => 48A for domestic use comes in at around 10 + 0.3*(48-10) = 22A for diversity, hence a 32A circuit would usually be considered OK and, length dependant, that might be fine for 6mm.

But if the planned use is not domestic, say commercial kitchen, or someone who acts like a professional chef doing parties at home, you might want to revise that up a little. Perhaps to a 40A circuit (or even 50A if worst-case is you expectation, but few dishes would stand every ring and oven on max thermostatic setting for any length of times).
 
Putting large loads on the ring is not a good idea!

If you are reaching the limit for already present radial circuit then options such as replacing with heavier wire or running a 2nd circuit are obvious better choices. 11kW => 48A for domestic use comes in at around 10 + 0.3*(48-10) = 22A for diversity, hence a 32A circuit would usually be considered OK and, length dependant, that might be fine for 6mm.

But if the planned use is not domestic, say commercial kitchen, or someone who acts like a professional chef doing parties at home, you might want to revise that up a little. Perhaps to a 40A circuit (or even 50A if worst-case is you expectation, but few dishes would stand every ring and oven on max thermostatic setting for any length of times).
Thanks PC for great explanation. Good to have my diversity calc confirmed also. Have already ordered 40amp for this so will go with this.
 
Thanks PC for great explanation. Good to have my diversity calc confirmed also. Have already ordered 40amp for this so will go with this.
Hopefully checking that the cable is 40A rated, not just the MCB :)
[automerge]1589494168[/automerge]
Just to add: cable route and what it implies for thermal insulation / hot zones / grouping factors have all to be considered, but you would have to look at the specific site for those.

Trying to work out where the cable went in an existing installation to try and judge those can be a challenge!
 
Last edited:
Hopefully checking that the cable is 40A rated, not just the MCB :)
[automerge]1589494168[/automerge]
Just to add: cable route and what it implies for thermal insulation / hot zones / grouping factors have all to be considered, but you would have to look at the specific site for those.

Trying to work out where the cable went in an existing installation to try and judge those can be a challenge!

It is a 6mm and is just running through under floor joists ?
 
It is a 6mm and is just running through under floor joists ?
then it's ref.method C and 6mm is rated at 47A. so you are OK with a 40A MCB. having said that, a 32A MCB is not likely to trip .even in a swicth on surge, as MCBs will take 1.45 x rating for some time.
 
It is not Method C as it is not clipped direct to a wall it is within a building void which makes Method B rating the cable at 38A.
where does that come from? B is in conduit or trunking. if it's between floors with no insulation, that part is in free air.
 
Last edited:

Reply to Why 2 hob ratings per ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top