Ryan Kavanagh

hi guys,

Just wanted some help with some course work for college. Any help is greatly apprecitaed.

Why should a low value earth fault impedance should be achieved for all circuts?

thanks
 
OK< in simple terms. think ohm's law. I=V/R. V is fixed at 240v (single phase) . the value of R ten determines the fault current. the lower the vale, of R, the larger the fault current. if you look at the time/current curves in app.3 of BS7671, you will see that the higher the fault current, the quicker the fuse/MCB will trip, thus isolating the circuit. the quicker it does this, the better.
 
so its importnat to have the low value earth fault impendance so the current is flowing freely and will be higher. it will then trip the circut breakers quicker under fault conditions as its got less current to increase to that trip point!

am i getting it now?
 
oh okay,

so its basically it can increase quicker and trip the breaker


Not increase quicker, but a higher value of current can flow, tripping the protective device in the required time.

Don't limit your answers to 'circuit breakers' etc.
 
Be careful of the terminology too. You need to refer to "Causing the operation of the protective device"
In an exam like 2391 terminology can get you a fail. Obviously if you're at a low level they may let you by because they know what you mean but it's good to get into the habit ofusing the corrct terms
 

Reply to why a low earth fault loop impedance in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top