why a low earth fault loop impedance

R

Ryan Kavanagh

hi guys,

Just wanted some help with some course work for college. Any help is greatly apprecitaed.

Why should a low value earth fault impedance should be achieved for all circuts?

thanks
 
OK< in simple terms. think ohm's law. I=V/R. V is fixed at 240v (single phase) . the value of R ten determines the fault current. the lower the vale, of R, the larger the fault current. if you look at the time/current curves in app.3 of BS7671, you will see that the higher the fault current, the quicker the fuse/MCB will trip, thus isolating the circuit. the quicker it does this, the better.
 
so its importnat to have the low value earth fault impendance so the current is flowing freely and will be higher. it will then trip the circut breakers quicker under fault conditions as its got less current to increase to that trip point!

am i getting it now?
 
Be careful of the terminology too. You need to refer to "Causing the operation of the protective device"
In an exam like 2391 terminology can get you a fail. Obviously if you're at a low level they may let you by because they know what you mean but it's good to get into the habit ofusing the corrct terms
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Ryan Kavanagh,
Last reply from
pencilpusher,
Replies
19
Views
18,475

Advert

Back
Top