hi guys,

Just wanted some help with some course work for college. Any help is greatly apprecitaed.

Why should a low value earth fault impedance should be achieved for all circuts?

thanks
 
If your earth loop is too low, then the overcurrent device will NOT be able to stop the fault the current, and in effect weld the MCB.

Very rare I might add, but might make you understand better.
 
Its like this. Ohms law.

230v with an earth loop impedance of 0.1 ohm. (Good)
230/0.1=2300A.

So 2300a of fault current will flow in the circuit.

Lets assume the circuit is protected by a BS60898 16a B type MCB

2300a in this particular circuit will disconnect almost instantly, and so comply with the 0.4 second disconnection time. The difficult to understand tables in the BGB will give you an exact time.

Now lets look at poor EFLI

230v/10ohm=23a.(Bad)

23a fault current in this circuit, again from the difficult to understand tables in the BGB, we can see that this circuit will disconnect in about 10,000 seconds, thats about 2.5 hours, so it does not meet the 0.4 second disconnection time. Bear in mind that current of about 80mA can kill you, then 23a for 2.5 hours wont be much of a laugh.

This is why we need a very low loop impedance and this is why the suppliers state TN 0.8ohm Ze, and TNCS 0.35ohm Ze as a maximum.

The figures i quote from the BGB may not be accurate, as i have done this off the top of my head, but you get the picture i hope.

Cheers..........Howard
 

Reply to why a low earth fault loop impedance in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top