On the 1st page it gives 0.36 as the Ze (twice in fact!). I can't spot where you mean for 0.36 Zs.
The confusion over the 1.06Ka is because the property has TNS earthing. As your profile says you are a trainee I'll elaborate a bit....(hang in there!)
The Ipf is the highest of prospective dead shorts of Live-Earth and Live-Neutral and as this property has TNS earthing the two will differ due to the different sizes of the two cables all the way back to the substation transformer. (If it were TNCS earthing then due to the neutral-earth link in the cut-out the values would be the same)
The path back to the transformer through the neutral has a lower impedance of 0.21 ohms (working backwards from 1060 amps) as it's a bigger wire. This makes sense.
So the maximum fault current Line-Earth is 638 amps (230/0.36) and the maximum fault current Line-Neutral is 1060A.
The installer recorded the higher of the two (correctly).