Hi, I'm hoping you can help me as I it's driving me insane!

So my electric keeps tripping when I plug my dryer in, now I know it's not a faulty dryer because it's the 3rd we've tried and it worked perfectly fine at a friend's for a week. My partner plugged a drill in last night and it tripped but worked after resetting the fuse board. The fuse board has an rcd if that helps any?

I have just un plugged everything and then tried plugging dryer in and it still tripped, whyyy is it doing this? I've tried it in different sockets, even a different room and still the same turn it in wait a few seconds and the whole electric has tripped.

Any help would he great appreciated. Tia
 
an rcd socket is what it sounds like... an rcd built into a regular wall socket... so that oinly what is plugged into that socket is protected by the rcd.

An rcbo is basically an rcd built into a circuit breaker. The entire circuit is protected, but not the rest of the installation.

An rcd mainswitch is fitted into your distribution board and that one rcd protects a group of circuit breakers. You may have one that protects all sockets in your house, or you may have a spliut board, where there are two rcd 's covering half the house each.

It would be helpful to know what you have in your house, and what your friend has as well. From there we can maybe suggest some fault finding procedures
 
Could just be a faulty RCD. Had one myself last couple of weeks that was tripping under 9mA
Or
It could just be that the accumulated earth leakage currents on the system is excessive for the RCD and that no particular item is faulty!
I did have a dryer that was working fine until it broke but it was 10 years old so can't grumble. But that would mean the circuit isn't being overloaded right?
an rcd socket is what it sounds like... an rcd built into a regular wall socket... so that oinly what is plugged into that socket is protected by the rcd.

An rcbo is basically an rcd built into a circuit breaker. The entire circuit is protected, but not the rest of the installation.

An rcd mainswitch is fitted into your distribution board and that one rcd protects a group of circuit breakers. You may have one that protects all sockets in your house, or you may have a spliut board, where there are two rcd 's covering half the house each.

It would be helpful to know what you have in your house, and what your friend has as well. From there we can maybe suggest some fault finding procedures

an rcd socket is what it sounds like... an rcd built into a regular wall socket... so that oinly what is plugged into that socket is protected by the rcd.

An rcbo is basically an rcd built into a circuit breaker. The entire circuit is protected, but not the rest of the installation.

An rcd mainswitch is fitted into your distribution board and that one rcd protects a group of circuit breakers. You may have one that protects all sockets in your house, or you may have a spliut board, where there are two rcd 's covering half the house each.

It would be helpful to know what you have in your house, and what your friend has as well. From there we can maybe suggest some fault finding procedures
Thanks for the reply, I have one rcd in my house and my friend has a split with 2.
 
Just unlikely but my least favourite thing is a freezer. While you unplugged everything - did you unplug fridge/freezers.

most of your sockets will be on a ring.
Did you try upstairs as well as downstairs as they are often on separate ring circuits?

Another circuit - could be an outbuilding e.g. garage.
 
Just unlikely but my least favourite thing is a freezer. While you unplugged everything - did you unplug fridge/freezers.

most of your sockets will be on a ring.
Did you try upstairs as well as downstairs as they are often on separate ring circuits?

Another circuit - could be an outbuilding e.g. garage.
Hi,

Yes I unplugged the fridge freezer and turned all upstairs off too as well as the loft. I have disconnected the outside sockets from the fuse board at the junction box.
 
Another thing that may be easy to try.

I had a socket RCD near a freezer and it tripped when I used a drill and it tripped the main RCD for the house.

replaced socket with a non rcd one and used the drill plugged into an extension cable with an RCD plug into the same socket.

all worked fine and no RCD tripped.
If you happened to have an extension cable with an rcd , it might be e we orth trying.
 
I would recommend contacting another electrician to do some more testing.

Faults like this can sometimes be difficult to find, but they are very very difficult to find without having the correct test kit and knowing how to use it. An insulation resistance tester is almost essential for finding why an RCD is tripping, it's the first tool I reach for every time I get sent to RCD tripping issues.

As mentioned earlier the fault could be elsewhere on another circuit and not a fault with the dryer. An RCD close to tripping can be taken over the edge when high loads like dryers and vacuum cleaners are switched on.

RCDs can sometimes be faulty but from experience all the faults I've seen have been RCDs not tripping when they should.
 
My sister had this issue a while back.
Ended up being an outside light on a fused spur wired into the ring main.
It was letting water in!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottinghamshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Why does my electric keeps tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30
Unsolved
--

Advert

Thread statistics

Created
Tan1992,
Last reply from
westward10,
Replies
30
Views
5,010

Advert

Back
Top