Mk-blg

DIY
Joined
Sep 11, 2024
Messages
3
Reaction score
4
Location
Ireland
I've had to have my immersion switch replaced 2-3 times over the last few years, the guy I had do it isn't a professional so I'm thinking he's wiring it wrong? I wired this one myself based on what way he had it wired the last time. It seems to be the blue wire that gets warm and melts everything else.

[ElectriciansForums.net] Why does my immersion switch keep melting?
 
What's the deal with the short link in the Lout terminal?
 
What's the deal with the short link in the Lout terminal?
Link is to a 2W 20A switch, that selects between two immersion heater elements.
The green/yellow used for the link looks a little undersized, so might warm things a little, and it looks like the back box might be a bit short of room, but other than that there's nothing wrong that stands out.
 
Link is to a 2W 20A switch, that selects between two immersion heater elements.
The green/yellow used for the link looks a little undersized, so might warm things a little, and it looks like the back box might be a bit short of room, but other than that there's nothing wrong that stands out.

Ah just saw the g/y earth colours and didn't look much further.

Usual suspects would be cheap/old accessory and/or poorly made connections.
 
When you rewired the last switch, you say the blue wire had overheated - was the copper a darkened/ oxidised colour?
And were other wires affected by heat?
The discolouration can give poorer surface conductivity, and the heat can make the copper softer, both of which can lead to a poorer quality termination if the overheated switch is replaced without dealing with the damaged cable ends.
It's best, if you can, to cut the wire(s) back so that you get to shiny unoxidised copper to make new joints with.
If you did this when you last changed the switch, then I would blame the switch for the problem!
 
When you rewired the last switch, you say the blue wire had overheated - was the copper a darkened/ oxidised colour?
And were other wires affected by heat?
The discolouration can give poorer surface conductivity, and the heat can make the copper softer, both of which can lead to a poorer quality termination if the overheated switch is replaced without dealing with the damaged cable ends.
It's best, if you can, to cut the wire(s) back so that you get to shiny unoxidised copper to make new joints with.
If you did this when you last changed the switch, then I would blame the switch for the problem!
I didn’t cut them back as much as I probably should have. I will try that with the next switch. Thanks
 

Reply to Why does my immersion switch keep melting? in the DIY Electrical Advice area at ElectriciansForums.net

Similar threads

My experience with commercial lighting is when the fixture is ordered or bought the specs should say 120/277. Then their wiring diagram should be...
Replies
7
Views
478
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
192

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top