I have been posed the question (by another electrician) "Why do people fit pull-cord switches in their bathrooms (for a shower)?" He challenged me to find a regulation that requires such a device be fitted.
The best I could come up with was 537.2.1.1 Every circuit shall be capable of being isolated from each of the live supply conductors ....
Is there a more specific/relevant regulation concerning this issue?
 
Pull cords are fixed to the ceiling which tends to take them out of the zones so that you can fit them near the shower.
A plate switch near the shower would not be permitted.
Saves power because other wise that little red light on the shower would be on all the time if there was no switch!

Follow the manufacturers instructions which tend to say must have a double pole isolator.
 
I remember going to a job to replace a faulty electric shower and the customer told us about how she never switched off the isolator one day she went to work came home in the evening to find the shower going full pelt with the shower curtain pulled back and the shower head pointed out of the bath spraying on to the bathroom floor And flooded the flat I guess she must have had a power surge and the the shower kicked in. Strangely enough I think she turns off the isolator after using the shower now.
 
The MCB will act as an isolator and most shower panel switches will act for the switching.

If the MCB or the panel switch is not double pole then for a TT system you will need DP isolation/switching.

If the manufacturer though ask for a double pole isolation and as above then again a DP isolator/switch will need to be fitted.

Apart from above, then there is no need to fit one. It is like a lot of things in our trade, it's seems to be the done thing.

Personally I do fit them, but if I found that one was not fitted, and it did not contravene the regs, then I would not worry to much
 
Well the proper thing to do.....would be to fit a flush switch outside the bathroom, because pull cords are the traditional MK cooker switch of the bathroom world

:shades_smile:
 
As far as the Regulations are concerned, try Regulation 554.3.3, which covers 'Water heaters having immersed and uninsulated heating elements' (no, NOT electrode boilers, we are talking 'immersion type' heaters!).Electric showers contain a small tank with an instantaneous immersed water heater in it, and hence come into this category.

It states " The heater or boiler shall be permanently connected to the electricity supply through a double-pole linked switch which is either separate from and within easy reach of the heater or boiler or is incorporated therin".

If you then check Regulation 701.512.3, erection of switchgear, control gear etc etc, you will see it states that

"The following requirements do not apply to switches and controls which are incorporated in fixed current-using equipment suitable for use in that zone or to insulating pull cords of cord operated switches".

Those are the Regs that probably cover your question. Other factors like isolation, safety etc have been mentioned by other contributors already so I wont add any more. Hope that helps

The Oracle
 
Do showers have uninsulated heating elements?

And to follow up Top Cats comment, does anyone know a pull cord isolator that isn't a complete pig to get 10mm2 into? I can't help thinking there would be a good market for one!
 
Do showers have uninsulated heating elements?

And to follow up Top Cats comment, does anyone know a pull cord isolator that isn't a complete pig to get 10mm2 into? I can't help thinking there would be a good market for one!
Its not to difficult if you use a deeper than standard box.
 
As far as i know, those with experience of shower installation use the 50A Crabtree pull switch, which also facilitates easier testing by taking the neon light out of circuit by dropping the switch from the back box...

If for no other reason, the inclusion of a readily accessible isolating pull switch for anyone using the shower as an emergency means of disconnection is to say the least ''prudent'' and well worth the effort!!!
 
i once toyed with idea of installing a contactor in the supply to a shower at the DB/above bathroom with a operating switch located next to bathroom door
 
As far as the Regulations are concerned, try Regulation 554.3.3, which covers 'Water heaters having immersed and uninsulated heating elements' (no, NOT electrode boilers, we are talking 'immersion type' heaters!).Electric showers contain a small tank with an instantaneous immersed water heater in it, and hence come into this category.

It states " The heater or boiler shall be permanently connected to the electricity supply through a double-pole linked switch which is either separate from and within easy reach of the heater or boiler or is incorporated therin".

If you then check Regulation 701.512.3, erection of switchgear, control gear etc etc, you will see it states that

"The following requirements do not apply to switches and controls which are incorporated in fixed current-using equipment suitable for use in that zone or to insulating pull cords of cord operated switches".

Those are the Regs that probably cover your question. Other factors like isolation, safety etc have been mentioned by other contributors already so I wont add any more. Hope that helps

The Oracle

Well oracle I think you'll find that

1 Showers are not classed for 554.3 the same as kettles are not

2. 701.512.3 again as nothing to do with requirements for DP separate switches for showers, as this reg also includes the use of a pull cord switch for lights
 

Reply to Why fit a pull-cord switch for a shower? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top