When I say changed in 18th I probably being a bit broad. Hager have changed their RCD type and assumed it was something to do with the 18th but prob isntNot aware that they’ve changed.
It could be something to do with some cease to work if some types of d.c. voltage are present.
This looks great thank you very much !this will explain it all RCDs and the 18th Edition - https://www.voltimum.co.uk/articles/rcds-and-18th-edition
when you think about the number of devices such as laptops, flat screen tvs, smart devices, the list is endless that take mains ac and via transformer down rate it to dc then the potential for faults that the usual rcds wouldnt detect is present. how dangerous it is remains to be seen.
A supplier asked me about 100Amp rcds due to 18th edition, i told him i was unaware of this, which i am. Does it only apply to single upfront rcd on 100A supplies not split?RCDs have not changed, however.
Hager have decided to use type A RCDs in their split load boards, as well as uprating them to 100amp.
According to Hager there were a few instances last year where AC RCDs were returned to Hager due to failing to trip. They determined it was because of a high number of DC power adapters/usb charging sockets on the circuit, which creates a higher earth leakage which can also affect RCD trip times. So now they ship with type A RCDs due to better capability/ selectivity across the board. There is nothing wrong with AC type RCDs in most cases though.
Your hear different story's from the folk down the wholesalers, though im sure and some mis-informed Hager reps might get confused.
Really its down to the designer to select what type of RCD is best.
They up-rated the rating of the RCD to comply with a different regulation, I believe there is a thread on here discussing it more in depth.A supplier asked me about 100Amp rcds due to 18th edition, i told him i was unaware of this, which i am. Does it only apply to single upfront rcd on 100A supplies not split?
A supplier asked me about 100Amp rcds due to 18th edition, i told him i was unaware of this, which i am. Does it only apply to single upfront rcd on 100A supplies not split?
Unless adding the mcbs protected by one rccb doesn’t exceed the rating of the rccbI thought they now had to be rated not less than the upfront fuse?