Does anyone know why RCDs have changed in type in the 18th. Someone told me it was some5hing to do with DC faults? What type were they and what are they now?

Thanks

Spud
 
A supplier asked me about 100Amp rcds due to 18th edition, i told him i was unaware of this, which i am. Does it only apply to single upfront rcd on 100A supplies not split?
This reply from Essex to my question earlier in the week pretty much covered it :
Ok so this was covered in my 18th update course. Your supplier is 100% correct.

Reg 536.4.3.2 and 536.4.202 are the relevant regulations and basically say that RCCBs must be selected so that they are greater than or equal to the downstream circuits after diversity has been taken into account. However it also goes on to say that diversity alone cannot be used to determine RCCB ratings and that we must take into consideration manufacturers instructions.

BEAMA have told us that two methods can be used:

Method 1:
ensure that the rated current of the sum of the downstream MCBs do not exceed the rated current of the switch or RCCB when installed within the consumer unit.

Method 2:
ensure that the rated current of the switch or RCCB in the related assembly circuit in the consumer unit (Inc) stated by the assembly manufacturer, is not less than the rated current of the upstream overcurrent protective device (OCPD). For a domestic installation this is likely to be the cut-out fuse rated at 60 A, 80 A or 100 A.

So if you have a small 2 way DB with two 6A lighting circuits on you can use a 63A main switch or RCCB regardless of what the upstream OCPD is as the total rated current of the downstream devices are 12 amps and the 63A RCCB is greater than that and the DB cannot be added to.

However if you had a 10 way DB with 3x 32A then this means the total current of the downstream devices is 96 amps so the RCCB would not be compliant with BS7671: 2018 if the upstream OCPD was over 63A.
If the upstream OCPD was 60A you could put whatever you wanted downstread as the 63A RCCB or main switch is protected by the 60A OCPD.
 
Maybe the suppliers could go back to doing OCPD in ratings of 5amps. Would make it easier to use method 1.
30A+30A+15A+5A= 80A on each RCD and then any other circuits on an RCBO.

So how would we code a 17th edition board with a bedroom RFC, a living room RFC, dedicated boiler cct, a lighting circuit and a spare way on a 63amp RCD?
 
Maybe the suppliers could go back to doing OCPD in ratings of 5amps. Would make it easier to use method 1.
30A+30A+15A+5A= 80A on each RCD and then any other circuits on an RCBO.

So how would we code a 17th edition board with a bedroom RFC, a living room RFC, dedicated boiler cct, a lighting circuit and a spare way on a 63amp RCD?
No more than a C3 in my opinion if the rccb shows no signs of thermal damage which ,in probably most cases will show none after all we used to apply diversity alone of the final circuits protected by a single rccb.
It’s hard to imagine that on a single phase domestic dwelling that 80 amps plus will be drawn at any one time.
 
Last edited:

Reply to Why has RCD type changed in 18th edition? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Do some of the free online tests. Get used to using the book. After doing this I passed mine easy enough.
Replies
8
Views
2K
  • Question
My older card has it but my newer card doesn’t
    • Like
Replies
1
Views
596

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top