Does anyone understand the logic of 'mandating' 25mm meter tails when upgrading a CU, when the sizing of other cables are left to the electrician's discretion?

I'm again having to explain to a little old lady with not a lot of money that she's need new meter tails with with tiny 6-way board, for her tiny 2-bedroom flat.

Massively cooking range to feed? Nope! 10.8Kw Powershower? Nooooh!

When copper is becoming an increasingly rare resource shouldn't we be fitting what's needed?

My guess is that the IET are simply 10 years out of date, plus someone somewhere calculate the specification, then a sub committee adds 10% to that, and the main committee thinks - let's be in the safe side, and adds another 10%.

Craziness gone mad!!!

(Rant for the day over - thank you for listening)
 
The DNO's local to me have required 25mm² tails for a long time now the last time I can remember using 16mm² tails was around the early eighties

On all the sites I've seen where the meter has been changed recently the cut out to meter tails have been changed to 25mm²

May be the thinking is "what will do a lot will do a little" also as we all know there is no chance of the DNO's fuse blowing at any where close it's rated value so the larger tails will cope better with the potential overload beyond the fuses value
 
Likewise, and I wouldn't dream of using anything other than 25mm+ just to not get the grief and the argument, but it does make you think that there are an awful number of CU replacements going on where the tails are being replaced without any technical justification.
 
That's exactly my complaint. The 'powers that be' simply add a little more contigency into everything because that's easier than updating the 19th century technology underpinning today's wiring regs. Current MCB and RCD 'technology' could be replaced with something vastly more effective and accurate, but the entire industry is geared to churn out the things for a couple a quid apiece, and no one wants to invest in developing and marketing alternatives. My other beef ( oh, dear, second rant of the day coming on) is that while cables have got thicker (and total loads have generally gone down) the casings for CU and isolators, etc have got thinner and cheaper. It won't be long before we left with a bunch of breakers wrapped up in a 'plastic bag', wafting around in the air on top of a couple of rigid meter tails.
 
Likewise, and I wouldn't dream of using anything other than 25mm+ just to not get the grief and the argument,

That's it in a nutshell for me. With the proviso that as long as you have the knowledge (or the professionalism to want and gain the knowledge) as to why what you're fitting isn't strictly necessary then it's OK.

A similar situation IMHO to the "it must be RCD protected, and if it is all's well in the world". I've been to quote on a couple of jobs in the last few weeks where the customer has been told "It must have an RCD" or "You need a new CU" when neither is true. I just can't make up my mind if it's an excess of greed, or a shortage of knowledge driving them to tell customers such things.
 
That's it in a nutshell for me. With the proviso that as long as you have the knowledge (or the professionalism to want and gain the knowledge) as to why what you're fitting isn't strictly necessary then it's OK.

A similar situation IMHO to the "it must be RCD protected, and if it is all's well in the world". I've been to quote on a couple of jobs in the last few weeks where the customer has been told "It must have an RCD" or "You need a new CU" when neither is true. I just can't make up my mind if it's an excess of greed, or a shortage of knowledge driving them to tell customers such things.
well any work we do (my boss n i) that requires additional protection by means of RCD....we just fit a garage board...fed either from a spare way in the existing c/u.......or henley...either way you dont need to be fitting a complete new c/u as firstly you will need to inspect and then test the whole install again...( a can of worms)....and secondly only work you do needs to comply with the current edition of BS7671.....
 
I havent read all the posts!! but when I did my 16th edition and test and connect course years ago I was told that even though you may have a 60/80 Amp head at the time, the DNO may upgrade their service to 100 amp, therefore its prudent to fit 25mm tails.
 
I havent read all the posts!! but when I did my 16th edition and test and connect course years ago I was told that even though you may have a 60/80 Amp head at the time, the DNO may upgrade their service to 100 amp, therefore its prudent to fit 25mm tails.
and if you do your diversity calcs for the CU?.....100% of the highest load then 40% of the rest combined?..probably wont be 100A....and dont forget you can clamp it n all....bet you dont get anyware near 80A never mind 100A....
 
Totaly agree Glennspark, if you do get near 100A in a domestic setting I would hate to see what the quaterly bill was!!! and 25mm just dont bend as easy as 16mm and im sure the design of most the domestic stuff aint designed for 25mm, all the main switches seem to destort and argue.. but nothing a hammer cant fix "I will get that tail in":hammer:
 
well any work we do (my boss n i) that requires additional protection by means of RCD....we just fit a garage board...fed either from a spare way in the existing c/u.......or henley...either way you dont need to be fitting a complete new c/u as firstly you will need to inspect and then test the whole install again...( a can of worms)....and secondly only work you do needs to comply with the current edition of BS7671.....

I recently had to do work on a shower circuit and was going to do a two way wylex with main switch and 40A RCBO. Instead though, I discussed with the client and agreed to fit a 5 way board. My reasoning was that at any point in the future they could have an individual circuit tested and dropped in AND protected with a 30mA RCBO. If there was any fault finding to be done then there would be no interuption to their installation.
 
I've wondered about this as well. I've got a CU change coming up in a house with 16mm tails. I am tempted to just fit 25mm tails from the meter to the CU because it's a no brainer, it's not that much hassle and is probably the safest option from a part P assessment point of view, even if it is not really necessary from an electrical point of view, but the only thing that puts me off this approach is DNO seals on the meter connections. How do most sparks deal with that?
 
well you can always replace tails but how about showing your assessor how you do diversity calcs...for current using equipment/connected loads as well as C/Us.....that would be good wouldn`t it....;)
 
well you can always replace tails but how about showing your assessor how you do diversity calcs...for current using equipment/connected loads as well as C/Us.....that would be good wouldn`t it....;)

I preferred the look of the brand new 25mm tails in the CU I had fitted but wait... Nice new sparkly seals too... Now how does that work? ;)
 
As an eBay Associate we earn from qualifying purchases.
but the only thing that puts me off this approach is DNO seals on the meter connections. How do most sparks deal with that?

do the maths and leave the 16mm in if ok.

if dno want to come along at a later date and up to 100A fuse thats their look out just make sure you comply with your work and leave them meter seals alone!!
 

Reply to Why oh why 25mm meter tails? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top