I recently installed a photovoltaic solar system for a customer but there seems to be a problem with on of the breakers.
Here is a bit of context: The panelboard is a 100A main/125A bus 3ph 480V. The sum of the breakers is 120A (30,30,30,15,15) and each breaker is connected to an inverter.

What happened was when we installed the most recent 15A inverter, the breaker almost immediately tripped and the inverter was virtually destroyed. We quickly found that the inverter was actually a 208V, not 480V... We then replaced it with the correct inverter and reset the breaker. This worked fine and the system ran smoothly for about 4 months. But just a few days ago the breaker again tripped but this time tripped the main breaker along with it, and again damaging the inverter. Now we are stuck thinking why this happened.

Right now we have a few ideas but are not quite sure:
Is the sum of all the breakers too high for the panel to handle?
Or maybe the breaker was damaged and weakened the first time and finally completely failed the second time?
 
I recently installed a photovoltaic solar system for a customer but there seems to be a problem with on of the breakers.
Here is a bit of context: The panelboard is a 100A main/125A bus 3ph 480V. The sum of the breakers is 120A (30,30,30,15,15) and each breaker is connected to an inverter.

What happened was when we installed the most recent 15A inverter, the breaker almost immediately tripped and the inverter was virtually destroyed. We quickly found that the inverter was actually a 208V, not 480V... We then replaced it with the correct inverter and reset the breaker. This worked fine and the system ran smoothly for about 4 months. But just a few days ago the breaker again tripped but this time tripped the main breaker along with it, and again damaging the inverter. Now we are stuck thinking why this happened.

Right now we have a few ideas but are not quite sure:
Is the sum of all the breakers too high for the panel to handle?
Or maybe the breaker was damaged and weakened the first time and finally completely failed the second time?
What solar experience or, qualifications do you currently posses Epaday?
 
I recently installed a photovoltaic solar system for a customer but there seems to be a problem with on of the breakers.
Here is a bit of context: The panelboard is a 100A main/125A bus 3ph 480V. The sum of the breakers is 120A (30,30,30,15,15) and each breaker is connected to an inverter.

What happened was when we installed the most recent 15A inverter, the breaker almost immediately tripped and the inverter was virtually destroyed. We quickly found that the inverter was actually a 208V, not 480V... We then replaced it with the correct inverter and reset the breaker. This worked fine and the system ran smoothly for about 4 months. But just a few days ago the breaker again tripped but this time tripped the main breaker along with it, and again damaging the inverter. Now we are stuck thinking why this happened.

Right now we have a few ideas but are not quite sure:
Is the sum of all the breakers too high for the panel to handle?
Or maybe the breaker was damaged and weakened the first time and finally completely failed the second time?
Ep I have seen breakers that won’t trip even it went phase to phase so yes that’s possible. When it comes to sizing breakers and you look in the panel and start adding the sum of all the breakers exceed the main breaker is because what you have what is called a calculated load ( breakers ) and then you have connected loads on an average day your panel is probably pulling 30 amps because all the breakers are not pulling current at the same time. As with the problem that’s causing the inverter to fry and I’m assuming it’s the same one something just isn’t wired right. I don’t know enough about solar work to advise you but we have a solar power forum. They should be able to help you sorry
 
It's far more likely that a fault occurred in the inverter which caused an overcurrent which tripped the breakers, not a tripping breaker causing the inverter to develop a fault.

It is likely that both breakers operated due to a lack of selectivity/discrimination.
 

Reply to Why would the Main breaker trip? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

  • Question
How did it go?
Replies
12
Views
2K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top