Is This is an America code [NEC] code thing only? Or does 17th edition or IEC
have the same thing?
A wire runs between 2 panels is rated to carry 400 amps.
Its fed from a 600A breaker on the line side, and has a 400 Amp
breaker on its load side [the panel being fed from the other one].
Under NEC, we would say thats a code violation because
"a wire is only protected by its line side [feed side] breaker."
Meaning the correct breaker on the wire's load side doesnt
count at protecting the wire.
does 17th edition or IEC say the same thing?:confused:
 
The 17th edition says “ a device for protection against overload shall be installed at the point where a reduction occurs in the value of the current carrying capacity of the conductors” It does however then allow exclusions “The device protecting the conductor against overload may be installed along the run of that conductor“ followed by a series of conditions one of which is the max length of 3metres. This, I believe, is to allow for the branching from a riser to be fused in a convenient position away from the riser with a reduction an CSA of the branch cable to that of the riser.
Not exactly the scenario you describe but as close as the regulations get.
Hope above is of help
 

Reply to WIRES BETWEEN PANELS PROTECTED ON LINE SIDE ONLY, not by load side breaker? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Hi There How did you get on with your basement project?
Replies
1
Views
1K
  • Question
How did it go?
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top