Hi...
The website you need is Boat Safety Scheme - Home
This is the organisation that examines boats on behalf of the navigation authorities for inland waterways which BW is just part.
I know because I am one of the examiners.
We are strict BUT the requirements are basic and not up to current standards.
eg. at the moment a boat with red and black single 230v wires in the same conduit as red and black 12v would pass!!!!
New boats should comply with the Recreational Craft Directive with ref to the ISO's i mentioned earlier.
 
'finally the big red book 709.411.4 page 193 says you cannot connect a boat to a TNCS supply'

now in the big green book it doesn't say that (pg 226), just says you cannot connect the PME to any metalwork.

So in the case of a narrowboat and a TNCS supply I can connect line and PEN but the hull should be Earthed otherwise ie earth rod?

In which case a galvanic isolator would be redundant, or if used would comply with the regs until there was a fault, when it then makes the earth connection.... but would then contravene this reg.

Or should the whole system just not be PME?


 
There was some new stuff out there about marina supplies.
but the boat itself should comply with the iso's mentioned earlier.
How it is then connected to the shore power is then the subject of the red and green books. And from what I have read, the boat "earth" CPC must not be connected to any suppliers earth. I'll dig out some more info.
 
This is my first post , so please be Gentle. I wired a friends Canalboat some time ago and for me it was a steep learning curve. I fitted a Stirling 3kVA inverter, sockets lighting, pumps heating , Nav Lights etc. To start me off I used a book called Marine Electrical and Electronics Bible by John C Payne. ( absolutely brilliant ). The two boards I used were Merlin Gerin, and used the MCB's for both the DC and AC; as the MG ones can be downrated for DC. I believe MG now do DC Breakers. For the wiring I used multi-strand YY cable as its very flexible ( but not quite the temperature rating of HR ), most boats are run in 6491X, even at Boatyards; problems waiting to happen! In the engine compartment I used Galvanised tray and Kopex to run all the circuits, keeps it very tidy.
For the Regulations, especially colour coding of cables refer to ISO 101339 ( small craft DC Installations ) and ISO 13297 ( small craft AC Installations ). If I can help in any way , let me know.
 
'finally the big red book 709.411.4 page 193 says you cannot connect a boat to a TNCS supply'

now in the big green book it doesn't say that (pg 226), just says you cannot connect the PME to any metalwork.

So in the case of a narrowboat and a TNCS supply I can connect line and PEN but the hull should be Earthed otherwise ie earth rod?

In which case a galvanic isolator would be redundant, or if used would comply with the regs until there was a fault, when it then makes the earth connection.... but would then contravene this reg.

Or should the whole system just not be PME?


The ESQCR:2002, Amt:2009, Regulation 9.4 states The distributor shall not connect his combined neutral and protective conductor to any metalwork in a boat or caravan. This is because if the supply neutral was to become disconnected from earth, the metalwork of the boat or caravan could rise to Line potential, assuming they are not independently earthed. Persons entering or exiting the boat or caravan would be at risk of electric shock.
 
Last edited by a moderator:
Like yourselves I am an Installation Electrician, but was asked by a friend to wire his Canal boat. With reference to using single strand 6491X, I see this as a retrograde step as it is only single core unlike YY cable or HR cable which is Double insulated. Single core cable with no protection can chafe on metalwork due to age and vibration and in some cases where I have seen solid core can break at terminations , and unless it is 105 degree rated is susceptible to temperature.
With reference to the Earthing, you should always fit an isolating Transformer or Zinc Saver in the Earth from your shore supply. I will admit this is more for Cathodic protection than it is for Earth Isolation. Also your ac Earth from the shore supply should be bonded together with the Battery Negatives to the hull of the Boat.
 
Ah hadn't thought of it as single core, :sleeping:

I just use arctic.

I get all the regs, recreational craft directive is the one to comply with, tags to BS stuff etc

What I'm pondering over is the earthing of the hull to a shore connection.... after a GI if fitted, a simple plug in connection.

The BMEA and RCD etc require the earth and 12v -ve to be bonded at one point on the hull.

BGB says the PME cannot connect to any metalwork (narrowboat hull)

So what does one do with the earth?
 
Ah hadn't thought of it as single core, :sleeping:

I just use arctic.

I get all the regs, recreational craft directive is the one to comply with, tags to BS stuff etc

What I'm pondering over is the earthing of the hull to a shore connection.... after a GI if fitted, a simple plug in connection.

The BMEA and RCD etc require the earth and 12v -ve to be bonded at one point on the hull.

BGB says the PME cannot connect to any metalwork (narrowboat hull)

So what does one do with the earth?

It is normal installation practice to convert the incoming Marina TN-C-S (PME) supply to TT earthing at the RCD protected berthing sockets. So when the vessel connects to the shore supply via a standard hook-up cable any vessel metalwork is connected to the local TT earth electrode and isolated from the PME earth terminal. Unless you have an isolating transformer fitted on board the vessel to isolate the electrical system on your craft from the shore supply system (or other method of galvanic isolation), corrosion through electrolysis could damage the vessel or adjacent craft. BS 7671:2008, Amt 1:2011, Section 709.
 
That makes sense.

So lets say the narrowboat stops at one of the many ramshackle boatyards with leads trailing from the sheds.

Said boater would assume its a PME supply he is plugging in to, would we recommend separating the earth and using his own earth spike...... doubling as a mooring pin perhaps?
 
Any supply offered to a boater for hook-up should NOT be PME. The hook-up service provider has a duty of care under the H&S legislation to ensure the service he/she is providing does not put the customer at risk.
 
MarkieSparkie is on the ball there. You should have an Isolating Transformer fitted to alleviate any problems with the type of supply at the Boatyard. There will always be an Earth connection returning from the boat , but this will be segregated from your 'own' ac installation.
The regulations also state that you must be able to identify Reversed Polarity, Power Available and Power On at the point of entry of the ac supply onto the boat from the shore supply, this is quite easy to do with a couple of indicating lamps. By doing this you will be able to see that polarity is correct when visiting different Boatyards.
To recap , you should have your external supply earth segregated from your onboard Earth.
 

Reply to WIRING A BOAT - what regulations do apply?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
885

Similar threads

I’d be more concerned about those blanking clips on the main CU.
Replies
24
Views
4K
Hi All, In need of some advice on what is and isn't allowed under regs. I'm extending a circuit in my house so I can install a socket on the...
Replies
0
Views
214

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top