Hi, This is an old thread now but Boats like the one discussed, need to be wired to ISO 10133 (DC) and ISO 13297 (AC).
contact me for more info.
contact me for more info.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss WIRING A BOAT - what regulations do apply?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
For the wiring I used multi-strand YY cable as its very flexible ( but not quite the temperature rating of HR ), most boats are run in 6491X, even at Boatyards; problems waiting to happen!
Hi just curious, in what way problems waiting to happen?
The ESQCR:2002, Amt:2009, Regulation 9.4 states The distributor shall not connect his combined neutral and protective conductor to any metalwork in a boat or caravan. This is because if the supply neutral was to become disconnected from earth, the metalwork of the boat or caravan could rise to Line potential, assuming they are not independently earthed. Persons entering or exiting the boat or caravan would be at risk of electric shock.'finally the big red book 709.411.4 page 193 says you cannot connect a boat to a TNCS supply'
now in the big green book it doesn't say that (pg 226), just says you cannot connect the PME to any metalwork.
So in the case of a narrowboat and a TNCS supply I can connect line and PEN but the hull should be Earthed otherwise ie earth rod?
In which case a galvanic isolator would be redundant, or if used would comply with the regs until there was a fault, when it then makes the earth connection.... but would then contravene this reg.
Or should the whole system just not be PME?
Ah hadn't thought of it as single core,
I just use arctic.
I get all the regs, recreational craft directive is the one to comply with, tags to BS stuff etc
What I'm pondering over is the earthing of the hull to a shore connection.... after a GI if fitted, a simple plug in connection.
The BMEA and RCD etc require the earth and 12v -ve to be bonded at one point on the hull.
BGB says the PME cannot connect to any metalwork (narrowboat hull)
So what does one do with the earth?