So my boss had the NIC inspector out the other day and he mentioned that wiring a ring in 2.5 is no longer acceptable. He stated that even wiring a ring in 4mm is now pushing it when it's installed in insulation.

We have always wired rings in 4mm as we wire large holiday homes. All my other sparky mates use 2.5..

I'm just wondering if anyone else has had this said to them and if it's just the NIC being really picky as usual.
 
Hi Will. and welcome to the forum !
Maybe they are talking about the effect of insulation? The cable for a 32A ring must have a rating of at least 20A and for cable floating loose in a cavity wall with insulation the 2.5mm is only 13.5A (Table 4D5, method 103). Even 4mm is only 17.5A. So either 2.5 or 4mm can work for a ring, but insulation can spoil it ...
 
Hi,wiring a ring final circuit,in 2.5 is perfectly acceptable.

Applying other factors,to that circuit,such as external influences,grouping,temperature,etc,is also acceptable.

Taking the two statements,separately,is not acceptable.

I hope NICCY,find my explanation...acceptable ;)
 
Surely it depends on the installation method and the rating of the MCB?
Nowadays ring mains often aren't required to carry 32A so if on a 20A breaker or even a 16A then 2.5mm maybe ok.
Its all down to the calculations.
I've just done a ring main for a loft conversion but was able to minimise the cabling contact with insulation. So it was largely surface mount in free air. But if it has to go in wall and be completely insulated then it depends on the calcs and the current required.
 
Harmonised or not wires?
 
So my boss had the NIC inspector out the other day and he mentioned that wiring a ring in 2.5 is no longer acceptable. He stated that even wiring a ring in 4mm is now pushing it when it's installed in insulation.

We have always wired rings in 4mm as we wire large holiday homes. All my other sparky mates use 2.5..

I'm just wondering if anyone else has had this said to them and if it's just the NIC being really picky as usual.

Hi, well is insulation is involved then yes he's right, it derate's the cable.
 
Oooo, don't let @Pete999 hear you call it that.

I've got fed up calling it a RFC and customers asking whats that. Easier to call it a ring main and they know what I mean.
 

Reply to wiring a ring in 2.5 is no longer acceptable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
370
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
335
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
372

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top