What I'm asking Tony is, will the contactor suffer any damage, if one or more of the phases are isolated?
It's been a while since I've had much to do with contactors, but I seem to remember that they could become damaged if any of the phases were out of balance, or disconnected for any reason.
 
Ahh, got what you’re on about now. If the contactor was feeding a motor then yes removing a fuse will causes problems with imbalance and the O/L’s will trip. But for a lighting circuit you have no O/L’s so a single fuse can be pulled to isolate 1/3 of the loading with no problem.
 
Thanks Tony, what about these latching types, that some one suggested being used?
 
More bloody trouble than they’re worth, same number of switch wires but two coils to go wrong and all the mechanical bits to jamb up! Don’t even think about it!
 
More bloody trouble than they’re worth, same number of switch wires but two coils to go wrong and all the mechanical bits to jamb up! Don’t even think about it!

I think you will find that most contactor maufacturers reccommend the use of latching contactors for lighting circuits, you're guessing they know.
 
Can someone suggest any books or material I can access for the wiring diagrams? I find visual aids a lot clearer then simply being told how to do it.

try the jtl electrical installations books, theres level 1 and 2, they have decent diagrams and also explain thing reasonably well, there about £20 each or you may be able to get them from the libary.
 
If you go with 3-phase lighting (single phase lights) you'll need to take separate neutrals back to the DB for each phase otherwise you'll need linked mcbs.
 
Thanks, Tony
Your diagram was helpful.

One more question....I will be bringing 3-phase+neutral via 6mm SWA into my CU.
In order to supply the contactor do I just tap-off from one of the supplies! ie Brown phase?

Regards zulfim
 
Thanks, Tony
Your diagram was helpful.

One more question....I will be bringing 3-phase+neutral via 6mm SWA into my CU.
In order to supply the contactor do I just tap-off from one of the supplies! ie Brown phase?

Regards zulfim

Firstly, you must protect the coil circuit with a 6A MCB, the coil will not load the circuit very much.
If its a 230V control coil, its any phase plus neutral otherwise you'll need to use 2 phases (400V).
 
As ackbarthestar says protect the switch and coil with a smaller MCB or fuse. Use phase and neutral for the control. 415V is not acceptable on a control switch.

NBP will probably shoot me down for this!
Only joking Paul if you read this.
 
As ackbarthestar says protect the switch and coil with a smaller MCB or fuse. Use phase and neutral for the control. 415V is not acceptable on a control switch.

NBP will probably shoot me down for this!
Only joking Paul if you read this.

Yep, absolutely correct don't use 400/415V on single pole two way light switching - better make sure when you order the contactor it has a 230V coil.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Wiring Diagrams
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
zulfim,
Last reply from
ackbarthestar,
Replies
27
Views
4,253

Advert

Back
Top