This is a old question from C&G 2330 which I have answers to but the explanations given refer to the old IEE regs. (pre 17th edition) so I am not confident that the things I have done are correct. Any help would be gratefully received.
A 230v, 6 kW single phase load is supplied by single core pvc cables in high impact pvc conduit fixed to the surface of a brick wall over a distance of 20 metres. The circuit is protected by a type C circuit breaker. The temperature is 35 degrees Celsius.
Determine
a. the design current
b. the installation method
c. the circuit breaker rating
d. the correction factor
e. the minimum cable rating
f. the minimum cable size.
I have the design current as 26A, and reference method B, circuit breaker at 32A but then I get confused as I don't think I need a correction factor for reference method B in this situation...